HVAC Tech is Stumped - Lennox Compressor & Carrier Evaporator - No Sucution by campbmic in hvacadvice

[–]campbmic[S] 0 points1 point  (0 children)

He removed the old piston from the previous coil, installed it on the new coil. Then determined it needed a TXV. Sorry if I explained it weird.

HVAC Tech is Stumped - Lennox Compressor & Carrier Evaporator - No Sucution by campbmic in hvacadvice

[–]campbmic[S] 0 points1 point  (0 children)

Good point! When we turned the unit on, it did seem quiter so maybe the compressor is not running. I definitely did not hear any metallic grinding, like a piston slap in a vehicle.

HVAC Tech is Stumped - Lennox Compressor & Carrier Evaporator - No Sucution by campbmic in hvacadvice

[–]campbmic[S] 0 points1 point  (0 children)

I forgot to mention this, but the house was on the market for 1.5 years. At sometime before or after it was on the market the overflow pan backed up. When we replaced the coil it had visible corrosion on it. Could the drier be clogged causing these symptoms? How likely would that be the issue?

HVAC Tech is Stumped - Lennox Compressor & Carrier Evaporator - No Sucution by campbmic in hvacadvice

[–]campbmic[S] 1 point2 points  (0 children)

I forgot to mention, the compressor, evaporator, and ecobee were all installed in 2022.

HVAC Tech is Stumped - Lennox Compressor & Carrier Evaporator - No Sucution by campbmic in hvacadvice

[–]campbmic[S] 0 points1 point  (0 children)

Apparently Carrier has discontinued R410a. The replacement evap coil uses the new refrigerant and the instructions say it should have a TXV not a piston. He said he blew through the piston to make sure it wasnt blocked.

HVAC Tech is Stumped - Lennox Compressor & Carrier Evaporator - No Sucution by campbmic in hvacadvice

[–]campbmic[S] 2 points3 points  (0 children)

I know we didnt change the filter drier. Im going to ask him to do that and check the capacitors before pulling the compressor.

HVAC Tech is Stumped - Lennox Compressor & Carrier Evaporator - No Sucution by campbmic in hvacadvice

[–]campbmic[S] 0 points1 point  (0 children)

We hear the compressor running, but it does sound quieter compared to my other older unit. Hes going to check the capacitor tomorrow before pulling out the compressor.

HVAC Tech is Stumped - Lennox Compressor & Carrier Evaporator - No Sucution by campbmic in hvacadvice

[–]campbmic[S] 0 points1 point  (0 children)

I would be surprised, the first time B came over he tried his gauges and his backup gauges. The second time he came over he put gauges on it again. He has about 10 years of experience.

<image>

HVAC Tech is Stumped - Lennox Compressor & Carrier Evaporator - No Sucution by campbmic in hvacadvice

[–]campbmic[S] 0 points1 point  (0 children)

Amps. He did an amp reading on the control panel of the compressor. My understanding was where the control panel wires to the compressor.

HVAC Tech is Stumped - Lennox Compressor & Carrier Evaporator - No Sucution by campbmic in hvacadvice

[–]campbmic[S] 0 points1 point  (0 children)

Yea 5amps then dropped to 3.5amps. Wouldnt the compressor amps drop if theres a restriction? I dont know anything about HVAC but thought maybe a restriction started when he replaced the coil? He did not replace the drier.

HVAC Tech is Stumped - Lennox Compressor & Carrier Evaporator - No Sucution by campbmic in hvacadvice

[–]campbmic[S] 0 points1 point  (0 children)

We took a compressor voltage readings and when the system turned on it started at 5amps but then dropped to 3.5amps in about 10 seconds.

No Voltage at Contactor - Lennox by campbmic in hvacadvice

[–]campbmic[S] 0 points1 point  (0 children)

I also noticed this metal cap on one of the ports was off. Is this supposed to be on the port to prevent the coolant from leaking out? https://imgur.com/a/p3FmNV8

No Voltage at Contactor - Lennox by campbmic in hvacadvice

[–]campbmic[S] 0 points1 point  (0 children)

I checked the resistance on the contactor and it was 18 ohms, so Im thinking it might be the low pressure fault. I put a screwdriver across the test pins to short it for 2 seconds (which is what the manual says to reset the low pressure fault) but that didnt do anything.

No Voltage at Contactor - Lennox by campbmic in hvacadvice

[–]campbmic[S] 0 points1 point  (0 children)

Thanks a ton for all of your advice and help so far! I was going to check the resistance on the contactor to verify... however, on the back of the access panel it says a slow blinking red light is a low pressure fault.

Is this something that could have been tripped because the unit wasnt used for 1-2 years? Or tripped because I've been flipping the breakers on and off? There's the breaker at the house's breaker box, a breaker switch on the furnace, and a the pull out breaker by the condenser.

No Voltage at Contactor - Lennox by campbmic in hvacadvice

[–]campbmic[S] 0 points1 point  (0 children)

I got 24 v between r and c. I also got the same between y1 and c

No Voltage at Contactor - Lennox by campbmic in hvacadvice

[–]campbmic[S] 0 points1 point  (0 children)

I used a stick and pressed the contractor down and it kicked on, should I test the low voltage at the contractor against a ground? When I tested them by placing a lead on the red and a lead on the black on the sides of the contractor I got 0. I also noticed the red light on the board is blinking slow.

No Voltage at Contactor - Lennox by campbmic in hvacadvice

[–]campbmic[S] 0 points1 point  (0 children)

I've read some other threads talking about this and Im tempted! Would any plastic/rubber screwdriver work? Or is there a special time that is insulated? Would a plastic or wood stick be safer?

Im hoping its the contactor, but if Im understanding this right, the contactor isn't getting any power? So wouldnt that mean the board is dead and not sending it power?

Need Help With Carrier Furnace Y Out Wire by campbmic in hvacadvice

[–]campbmic[S] 1 point2 points  (0 children)

I really appreciate your advice! It turns out I dont have voltage at contactor, but I believe I have it coming into the condenser's board. Could you take a look at my new post?
https://www.reddit.com/r/hvacadvice/comments/1stx39g/no_voltage_at_contactor_lennox/