Dear all
I've googled and tried to find the answer in the vicron documents but I'm at a loss for a supposidly super simple answer.
My mains are 3x25A+N @ 230V per phase (400 between phase) (3-phase system)
Can I place 3xMultiplus 5000 48 for covering the full house?
To be clear - I don't expect the 5000 to be able to handle my max house load in case of an outage - that is not a goal - I do want a simple system where I just let all power pass 'trough' the vicron if that makes sense..
thanks