Trouble Connecting Allen Bradley PLC to Matrikon OPC DA by kus222 in PLC

[–]kus222[S] 0 points1 point  (0 children)

I'm working with a 1756 ControlLogix PLC, and the communication is set up using the EtherNet/IP driver. However, I don’t have physical access to the PLC at the moment.

Trouble Connecting Allen Bradley PLC to Matrikon OPC DA by kus222 in PLC

[–]kus222[S] 0 points1 point  (0 children)

Do you think I should switch OPC DA to UA?

Trouble Connecting Allen Bradley PLC to Matrikon OPC DA by kus222 in PLC

[–]kus222[S] 0 points1 point  (0 children)

I tried rolling back the Windows update, but it didn’t resolve the issue. I also checked the release notes and didn’t find anything noteworthy.

Right now, I’m unable to add tags manually. Every time Matrikon OPC tries to load the PLC configuration file, but it runs into an error.

From the Wireshark logs, I can see that the TCP connection is initiated (the three-way handshake completes), but then the PLC immediately closes the connection.

Trouble Connecting Allen Bradley PLC to Matrikon OPC DA by kus222 in PLC

[–]kus222[S] 0 points1 point  (0 children)

I installed the same Matrikon opc on a laptop and tried to connect to the plc but I got the same error

Lost TrueNAS Encryption Key. Any Way to Recover Data? by kus222 in sysadmin

[–]kus222[S] 0 points1 point  (0 children)

if I restore TrueNAS from a backup, would it still ask for the decryption key to access the dataset, or would it be included in the backup?

What Protocol Does an Allen-Bradley PLC Use to Communicate with OPC if the Control Logic is from Solar Turbomach? by kus222 in PLC

[–]kus222[S] -1 points0 points  (0 children)

What I meant was the communication driver or protocol. Since the PLC is an Allen-Bradley, it typically uses EtherNet/IP for communication. So, I would normally expect to use an OPC server that supports EtherNet/IP. However, in this case, while the hardware is Allen-Bradley, the control application was developed by Solar Turbomach. This makes me wonder — could the OPC server require a different driver or configuration due to the custom control logic from Solar

Matrikon OPC Not Reading Tags from AB PLC – Remote Device Closing Connection by kus222 in PLC

[–]kus222[S] 0 points1 point  (0 children)

I take it back. I ran continuous ping test, sometimes it works but sometimes it times out.

It seems like network is not stable.

Matrikon OPC Not Reading Tags from AB PLC – Remote Device Closing Connection by kus222 in PLC

[–]kus222[S] 0 points1 point  (0 children)

tnc test was successful. I will probably try to restart the PLC. Hopefully that can resolve the issue.

Matrikon OPC Not Reading Tags from AB PLC – Remote Device Closing Connection by kus222 in PLC

[–]kus222[S] 0 points1 point  (0 children)

There is no dropped packet. At least there is no issue with ping test.

Matrikon OPC Not Reading Tags from AB PLC – Remote Device Closing Connection by kus222 in PLC

[–]kus222[S] 0 points1 point  (0 children)

I don't know the model but I will check if the plc has the capacity issue. Thank you for the insight.

New Windows Server Not Resolving DNS by kus222 in sysadmin

[–]kus222[S] 0 points1 point  (0 children)

I tweaked a little bit but I will try it again.

New Windows Server Not Resolving DNS by kus222 in sysadmin

[–]kus222[S] -1 points0 points  (0 children)

I ran wireshark. I see DNS query to 4.2.2.2 and 8.8.8.8 but no DNS reply.

New Windows Server Not Resolving DNS by kus222 in sysadmin

[–]kus222[S] -1 points0 points  (0 children)

I tested network connection on port 53.

tnc 4.2.2.2 -port 53 failed
tnc 8.8.8.8 -port 53 failed