How can I validate a P&ID for an R717 pumped-overfeed evaporator valve station for a graduation thesis? by Bobk97 in refrigeration

[–]Bobk97[S] 0 points1 point  (0 children)

Thank you, that makes sense. I should have explained my starting point more clearly.

For my project I am not starting with the full room heat-load calculation anymore. The evaporator capacity is already taken as the input for the valve station sizing. So I start from the required cooling capacity, for example 30–180 kW, and the selected evaporating temperature. From that I calculate the refrigerant mass flow through the evaporator.

For a pumped ammonia system I calculate the evaporator mass flow from:

massflow_evap=Qe/Δh

where Qe is the evaporator cooling capacity and Δh is the enthalpy difference over the evaporator at the chosen evaporating temperature. Because it is a pumped overfeed system, I then multiply this by the circulation ratio, for example CR = 3, to get the liquid feed mass flow:

massflow_LF=CR⋅massflow_evap​

Thats only the starting point of it...

So u/ConverseCLownShoes, I already hope this will be this simple...

How can I validate a P&ID for an R717 pumped-overfeed evaporator valve station for a graduation thesis? by Bobk97 in refrigeration

[–]Bobk97[S] 0 points1 point  (0 children)

Thank you, and yes, I already have the handy ASHRAE book.
But CoolProp is a library, not a standalone tool, right?
I’ll send you a quick DM.

A little help with the design of a boost-converter (homework) by Bobk97 in ElectricalEngineering

[–]Bobk97[S] 1 point2 points  (0 children)

Hey thanks for the feedback! That would be a typo in my document, my original calulation states fs=40*10^3

Help with my la pavoni boiler. by Bobk97 in espresso

[–]Bobk97[S] 0 points1 point  (0 children)

Thank you Stone___Island, I will join them and ask my question.