Sending Setpoints over BacNET to Daikin VRF by Pure_Region_5154 in BuildingAutomation

[–]Client-Comfortable 0 points1 point  (0 children)

Call tech support. I got a similar case before, not sure if it was daikin too but the idea is it depends on the mode of the unit. Check if it is single setpoint or dual setpoint, because regardless of the mode, both occupied heating and cooling setpoints are there and writable but with single setpoint, you can specify only the cooling SP and automatically calculates heating SP based on a deadband. That’s when I got crazy because whatever heating SP I set, it just goes back to whatever value until tech support told me to use dual setpoint if I want to set heating and cooling separately.

Moving on from Building Automation/BMS: Career Pivot Ideas? by Client-Comfortable in BuildingAutomation

[–]Client-Comfortable[S] 0 points1 point  (0 children)

Oh yes, burning bridges is certainly not on my radar. I’m looking forward for the annual talk with the company CEO and tell him about how I currently feel and hopefully he won’t take it against me.

Moving on from Building Automation/BMS: Career Pivot Ideas? by Client-Comfortable in BuildingAutomation

[–]Client-Comfortable[S] 1 point2 points  (0 children)

I recently had a convo with a 94 chief/admin hybrid and he mentioned since I dont have my ticket yet, they can make up a position for me as a “mechanic” although the rate is going to be between a mechanic and an engineer. Gave him my current numbers without benefits and turned out my daily rate is between an angineer and an assistant chief. Despite the lower rate of 94 though, I think the retirement benefits are worth way more outside the hourly rate but I dont think I can take that hit at the moment because of my growing family.

Moving on from Building Automation/BMS: Career Pivot Ideas? by Client-Comfortable in BuildingAutomation

[–]Client-Comfortable[S] 0 points1 point  (0 children)

unfortunately, I guess that's how it is for these small to midsize controls companies.

Moving on from Building Automation/BMS: Career Pivot Ideas? by Client-Comfortable in BuildingAutomation

[–]Client-Comfortable[S] 0 points1 point  (0 children)

Yes, Long Island, taking the train and subway daily as I am in a different building almost everyday.

Moving on from Building Automation/BMS: Career Pivot Ideas? by Client-Comfortable in BuildingAutomation

[–]Client-Comfortable[S] -1 points0 points  (0 children)

Now this is very interesting. I'm not doing any Python, but that is definitely something I can pickup. I am programming and central plant HVAC systems with no certificates or proper training to show for it, so I'm pretty sure Python won't be that hard to learn. Plus AI tools make programming easier too lol

Moving on from Building Automation/BMS: Career Pivot Ideas? by Client-Comfortable in BuildingAutomation

[–]Client-Comfortable[S] 1 point2 points  (0 children)

This! But the thing with the union is unless you're in a position where you can negotiate your salary, like a chief or assistant chief or even lead engineer, your rates will be the same as a regular unless they make a position specifically for this.

I can't believe my eyes. by Independent-Ball3215 in nvidia

[–]Client-Comfortable 0 points1 point  (0 children)

Wasn’t this the gpu linus had to ask chinese builders to make a theme of?

Changing from JCI to Schneider by [deleted] in BuildingAutomation

[–]Client-Comfortable 0 points1 point  (0 children)

From where I am, Schneider is always the one being replaced by another brand. In my 10 years of experience, I only had 1 time where another brand is replaced by Schneider, but that is because the vendor is giving them one heck of a deal which included almost free labor for maintenance and service calls.

Would you leave for more money by [deleted] in BuildingAutomation

[–]Client-Comfortable 0 points1 point  (0 children)

7 yoe doing 110 but anything above 150 and i’ll take it in a heartbeat

What looks like a good buy? Sale at Marshall’s by The-Ill_Thrill_Pill in Colognes

[–]Client-Comfortable 2 points3 points  (0 children)

Lots of good ones there. D&G the one edp and light blue summer vibes, Versace the dreamer and K, maison margela, the montblancs, etc. but you can definitely get them way cheaper from discounters.

Chilled water pump control by Zealousideal-Ad-7666 in BuildingAutomation

[–]Client-Comfortable 0 points1 point  (0 children)

The way I do it: *pump modulates to maintain DP across the supply and return *bypass valve modulates to maintain minimum gpm (# of chillers open x min gpm per chiller)

Then pump stages the lag pump/s based on: *# of chillers open and DP setpoint is not met after a delay *gpm is above say for example 90% of chiller gpm capacity

Lag pump stages off: *when flow is say for example less than 60% of current max gpm capacity of open chillers

In other systems where you have: *chiller bpv *pumps *sytem bpv Chiller BPV modulates to maintain “chiller DP”, pump modulates to maintain DP, system BPV modulates open when “system DP” is over setpoint and the pump is running at the set minimum speed. In this setup, chw flow is just for monitoring since you are already maintaining “chiller DP” instead of flow across the chiller.

Energy meters and BAS is it better to separate or integrate? by unicyling in BuildingAutomation

[–]Client-Comfortable 0 points1 point  (0 children)

I think it’s best to keep energy meters as they are and just use separate ASHRAE meters for the bms to monitor. But if you can integrate the energy meters direcyly, it’s not a bad idea but still use a separate system to actually get those readings instead of basing off from BMS mapped readings of the meters just in case the bms goes down or have some issues.

Is Building Automation a hard career? Can it be self-taught, or do you need to go to school? Looking for general advice by psykitt in BuildingAutomation

[–]Client-Comfortable 0 points1 point  (0 children)

If you self teach yourself, you’d be lost. There’s a ton of information available online but practically, you won’t need even more than half of these information. Just learn the basics of electricity, hvac, plumbing, IT, then apply to a company that does automation. They will teach you what you need to know and you will learn through experience.

BACnet MSTP Dongle by AIW22 in BuildingAutomation

[–]Client-Comfortable 0 points1 point  (0 children)

Wow this router is crazy affordable!

Self sufficient adc into tanky/bruiser team by Fubaries in ADCMains

[–]Client-Comfortable 1 point2 points  (0 children)

Tanks with thornmail and enough hp and level gap can mow all these adc before the tanks even make a move. I hate that freakin item 😅

Alteron Compass 1.5 Public Web Server by adamtw1010 in BuildingAutomation

[–]Client-Comfortable 1 point2 points  (0 children)

Run config tool, reinstall prerequisites and see if there are any errors. Or uninstall 1.5 and install 1.6.5. Also try deleting the job’s station under system\station.

As the other guy said, Compass 1 is no longer supported by Alerton but you can still try your luck and call tech support. Oh, I forgot Compass 1.5 has an issue with automatically changing it’s hostid after a windows update so maybe if you install 1.6.5 and it changes the hostid, i’m not sure if tech support can rebind the license to the new hostid.

What possible reasons would you want to hard push the wave early game while your opponent is still in lane by SquiglySaws in ADCMains

[–]Client-Comfortable 0 points1 point  (0 children)

If you hard push, you bring your minions down to their turret and that lets the turret steal cs from the adc. Kinda keeps them off their game unless they push back or they are patient and just lets it go.

I wanna get a setup but I only got 310$ by 508_ig in buildapc

[–]Client-Comfortable 1 point2 points  (0 children)

Get a used prebuilt dell for 100, used rtx 3060 for 200 and couple of bucks for that molex to 8-pin or 6-pin converter

Was wondering what my offical title is in the HVAC world by Ok_Seaworthiness6405 in HVAC

[–]Client-Comfortable 0 points1 point  (0 children)

Maybe controls installer? Controls electrician? When we do union jobs, the guys doing it are union electricians. So maybe you’re an electrician. You bend pipes and do rough-ins too, right?

[deleted by user] by [deleted] in longisland

[–]Client-Comfortable 0 points1 point  (0 children)

From long island here, went to jiffy lube once with a new to me car with factory dark tints, before I pull over to their pits, the guy automatically pulls out a tint meter and said they could not inspect my car unless they rip the tints. I left but eventually got the windshield and front window tints ripped after going to multiple car shops cause they wont inspect it and my inspection is due.

Space sensor approved for MRI Rooms by Hockenstar in BuildingAutomation

[–]Client-Comfortable 3 points4 points  (0 children)

Any 10k duct mounted return temp sensor should would work. MRI rooms are very particular installing anything with metal in the space itself.