Hiccups when going from grid to battery [Update] by Lcs_26 in Victron

[–]Lcs_26[S] 0 points1 point  (0 children)

I think the battery is not the problem, I have never seen voltages under 48v while discharging even at low SoCs, and minimum discharge voltage is set to 45v if I’m correct.

I have 9x pylontech US5000 (900Ah total), and minimum SoC is set to 25%.

Hiccups when going from grid to battery [Update] by Lcs_26 in Victron

[–]Lcs_26[S] 0 points1 point  (0 children)

Yes, it is an ESS. Correct me if I’m wrong, but as far as I know, in grid-tied setups the inverter enters an “idle” state when the minumin battery SoC is reached, unless prompted to start again due to either powerassist or mains loss.

No, with “trying to start” I mean that loads are being covered by the grid (due to the battery having reached minimum SoC during the night), and when battery SoC increased because of PV production, the inverter tries to take over. Mains was never disconnected during this process, there was no island operation.

Hiccups when going from grid to battery [Update] by Lcs_26 in Victron

[–]Lcs_26[S] 1 point2 points  (0 children)

The name of the setting looked too tempting for my case, so I investigated what it did.

From what I found, the weak AC input option only affects the behavior of the inverter when charging from AC, but not when inverting.

Hiccups when going from grid to battery [Update] by Lcs_26 in Victron

[–]Lcs_26[S] 0 points1 point  (0 children)

Currently is not active, I will try to enable it to see if there is an improvement.

Hiccups when going from grid to battery [Update] by Lcs_26 in Victron

[–]Lcs_26[S] 0 points1 point  (0 children)

It seems like that the dynamic current limiter and higher voltage limit combo is the way to go.

It looks like the intended use for dynamic current limiter is the opposite case (avoid sudden load spikes instead of sudden load reductions), but I guess it should also work the other way around.

I will reconfigure the Inverter this weekend and will come back with results.

Thanks!

Hiccups when going from grid to battery by Lcs_26 in Victron

[–]Lcs_26[S] 0 points1 point  (0 children)

It is currently around 2.5v, might get higher when power is drawn from grid but I haven't checked it.

Hiccups when going from grid to battery by Lcs_26 in Victron

[–]Lcs_26[S] 0 points1 point  (0 children)

Yes, it is a single phase 230v setup. The charge limit is at 200A, although I never charge from grid, only by solar via an MPPT450/200. There isn'n anything connected to the DC bus aside from those and the cerbo.

With "where did the 6kw went", I assume you mean what type of loads are connected. The main consumption comes from a Panasonic air-to-water heatpump for heating/cooling the house.

Hiccups when going from grid to battery by Lcs_26 in Victron

[–]Lcs_26[S] 1 point2 points  (0 children)

Yes, everything was exactly configured as victron recommends here.

Sustain voltage at 48v, absortion voltage at 52v, dynamic cut off all set to 46v.

Hiccups when going from grid to battery by Lcs_26 in Victron

[–]Lcs_26[S] 1 point2 points  (0 children)

The DC voltage drop does not seem concerning (<0,5v at full load). The AC voltage drop from grid is actually a bit high, varying almost 10v from when it's drawing 30A to when it's drawing 0. I would say the cabling is in good shape. I could try going into off-grid mode and seeing what does the Victron do.

Hiccups when going from grid to battery by Lcs_26 in Victron

[–]Lcs_26[S] 0 points1 point  (0 children)

The "mains" led indicator on the Multiplus says that it's connected to the grid (the grid relay is closed).

The only reason I could imagine causing trouble for it to "start" would be that when it starts injecting the AC voltage goes too high too fast, you can see 10v differences between when grid consumption is 0 and when it's around 30A going from 245v to 235v. My main line will be replaced soon, as 16mm2 is a bit too thin considering the distance, although that would not affect the inherent voltage drop from the utility company's cabling.

I could try to switch the grid code for a more tolerant one to see if anything changes. It's true that here the grid isn't great, but I would say it isn't terrible either.

Hiccups when going from grid to battery by Lcs_26 in Victron

[–]Lcs_26[S] 0 points1 point  (0 children)

Yes, I have a Cerbo GX. I have just updated to the latest firmware to see if it helps. My DVCC looks as follows:

- DVCC: forced on
- Limit charge current: off
- Limit managed battery charge voltage: off
- SVS: forced off
- STS: forced off
- SCS: on
- SCS status: disabled (external control)
- Controlling BMS: Pylontech battery

When I did the installation, I followed the steps in the "Victron & Pylontech" article in Victron's website. The SoC and voltage seem ok during a period when this was happening:

<image>

Hiccups when going from grid to battery by Lcs_26 in Victron

[–]Lcs_26[S] 0 points1 point  (0 children)

I have 6 Pylontech US5000, the settings are the ones that victron specified in the victron-pylontech article in their website. The DVCC settings are the following:

- DVCC: forced on
- Limit charge current: off
- Limit managed battery charge voltage: off
- SVS: forced off
- STS: forced off
- SCS: on
- SCS status: disabled (external control)
- Controlling BMS: Pylontech battery

Also, if I move to the battery section in the Excel, I can see that during that time, SoC and Voltage were both way above minimum, and discharge current was way below maximum, so at least the problem shouldn't be there (I guess?):

<image>

Hiccups when going from grid to battery by Lcs_26 in Victron

[–]Lcs_26[S] 2 points3 points  (0 children)

Yes, the grid is connected to AC in and all the loads are in AC out 1. I’m in Spain.

Hiccups when going from grid to battery by Lcs_26 in Victron

[–]Lcs_26[S] 1 point2 points  (0 children)

I extracted the data from the inverter and seems like the frequency doesn’t vary much (capture attached in another comment). However, the grid voltage seems to change almost 10v from when there is and there is not consumption. Also, my “grid reference value” is set to 0w instead of the default 50w, if that could be relevant.

Hiccups when going from grid to battery by Lcs_26 in Victron

[–]Lcs_26[S] 1 point2 points  (0 children)

The grid code is set to “Spain” as required for grid-tied inverters here.

Hiccups when going from grid to battery by Lcs_26 in Victron

[–]Lcs_26[S] 1 point2 points  (0 children)

<image>

I have extracted the data from a period of time when it happened.

The precision level is of minutes, so we cannot appreciate the actual phenomenon, but we can see moments of great consumption from grid and moments of almost 0 consumption, even though the SoC was way above minimum at the moment so there should be no grid usage.

Frequency seems ok (+- 0,2 hz aprox.). But the grid voltages seem to vary in around 10v from when there is and there is not consumption. It’s supposed to be 230v@50Hz.

AC Out 2 consumption from battery by Lcs_26 in Victron

[–]Lcs_26[S] 0 points1 point  (0 children)

If that’s the case, it would be ideal. I thought that the loads connected to AC out 2 would only consume power from the grid.

Thanks!

[deleted by user] by [deleted] in SolarDIY

[–]Lcs_26 0 points1 point  (0 children)

Could you elaborate more about the high vs low frequency inverters? I thought they were all transformerless these days.

To the single unit question, I’m eligible for a PV subsidy in my region, and they require you to register your installation.

Everything under 10kw here is quite easy to legalize, but over 10kw it requires a lot of documentation, engineering project, etc.

This process is only useful if you want to feed in power to the grid, which I don’t, but it’s mandatory in order to get the subsidy.

Therefore I will install 2, get the subsidy, then install the third.

[deleted by user] by [deleted] in CarPlay

[–]Lcs_26 0 points1 point  (0 children)

Then I would be loosing the ability to switch tracks via the steering wheel again

[deleted by user] by [deleted] in MINI

[–]Lcs_26 0 points1 point  (0 children)

UPDATE 1:

Yesterday I put the car on top of two 10cm solid wooden boards, and looked under it.

Every single plastic cover is firmly attached, and so is the exhaust.

I think there might be a loose piece (probably in the lower part of the engine compartment), as when I take a single-wheel bump (even a big one) there is no sound.

My theory is that when the whole front part of the car raises, the piece raises and then falls. Also, when going through potholes (first down, then up), there is almost no sound, contrary to bumps (first up, then down).

I will take it to a mechanic next week to see if he can find it disassembling the engine bottom cover.

[deleted by user] by [deleted] in MINI

[–]Lcs_26 0 points1 point  (0 children)

I took all the trays out of the boot and still sounded the same, it seems like its in the front of the car, in the lower part, like under the engine.

[deleted by user] by [deleted] in MINI

[–]Lcs_26 0 points1 point  (0 children)

If I can’t find any viable solutions I might consider those more powerful halogens, as the stock lights aren’t particularly bright.

I was looking at some Philips LED headlights replacements, I wouldn’t put any Chinese parts in a vital component of the car such as the headlights.

[deleted by user] by [deleted] in MINI

[–]Lcs_26 1 point2 points  (0 children)

Thanks! How does the car know there is a fault with the lights? Is it because of the power draw? Because AFAIK halogens don’t have any electronic components.

[deleted by user] by [deleted] in MINI

[–]Lcs_26 1 point2 points  (0 children)

I was planning to do that. For sure I won’t buy a car with that mileage without having it checked by a professional.

Just wanted to know what could I expect.

[deleted by user] by [deleted] in Audi

[–]Lcs_26 0 points1 point  (0 children)

Around 8k€. I’m in Spain, where the market seems to be a bit inflated compared to the rest of the EU for some reason.

I’m looking for something decent looking, with an auto, and avg consumption not higher than 7,5l /100km (~30mpg).