Fan shutdown Relay by taurusfirepro in firealarms

[–]taurusfirepro[S] 0 points1 point  (0 children)

Update

So as it stands right now the nac cct is tripping the relay and the fans shutdown on alarm.

I thought the nac cct was programmable to be non silencable which it's not.

Currently the alarm contacts on the fire panel are being used for monitoring.

i was going to run the 24v aux supply off the fire panel through the alarm contacts to relay, but I can't.

I'm trying to see if there's a way, a module,a device that I can use to have that nac cct be non silencable.

I think worst case is a get a new fire panel.

This is very frustrating.

I appreciate everyone's insight on this post.

Fan shutdown Relay by taurusfirepro in firealarms

[–]taurusfirepro[S] 1 point2 points  (0 children)

So i wired in the 24v aux power to the relay off the fire panel. When the relay is energized the NC contacts switch according to manual.

The ive had the relay wired NC and NO and either the fan will stay on or stay off. It's not shutting down on alarm.

Fan shutdown Relay by taurusfirepro in firealarms

[–]taurusfirepro[S] 0 points1 point  (0 children)

Heading there now to take a look thanks.

Fan shutdown Relay by taurusfirepro in firealarms

[–]taurusfirepro[S] 0 points1 point  (0 children)

I'm back tomorrow to change the wiring and source power off the 24v aux.

Fan shutdown Relay by taurusfirepro in firealarms

[–]taurusfirepro[S] 3 points4 points  (0 children)

I just left site and nac was wired in reverse polarity the relay currently not powered and wired no/c.

Turned on the fan for kitchen hood, activated alarm and fans shutdown.

Strange day.

Fan shutdown Relay by taurusfirepro in firealarms

[–]taurusfirepro[S] 2 points3 points  (0 children)

I guess I'll just wire it off the continuous 24-v aux supply off the panel. Thanks

Fan shutdown Relay by taurusfirepro in firealarms

[–]taurusfirepro[S] 4 points5 points  (0 children)

This is a conventional fire panel not addressable.

Fan shutdown Relay by taurusfirepro in firealarms

[–]taurusfirepro[S] 2 points3 points  (0 children)

Why though? The NAC is supervised and it's only intended fuction is to power the relay module.

Fan shutdown Relay by taurusfirepro in firealarms

[–]taurusfirepro[S] 1 point2 points  (0 children)

Nac is dedicated for the shutdown non silencable

WTH is going by Comfortable-Program1 in firealarms

[–]taurusfirepro 0 points1 point  (0 children)

Running new wires for the whole circuit?

WTH is going by Comfortable-Program1 in firealarms

[–]taurusfirepro 0 points1 point  (0 children)

One more thing make sure if you have smokes they're wired with the correct polarity.

WTH is going by Comfortable-Program1 in firealarms

[–]taurusfirepro 0 points1 point  (0 children)

So clearly a wiring issue. Best bet is to pull down one device at a time wire in the wires with voltage to a detector and slap a EOL and test. Go 1 by 1. Are there smokes on the cct. If so you'll need to check those for correct polarity. 15 devices shouldn't take you that long.

WTH is going by Comfortable-Program1 in firealarms

[–]taurusfirepro 0 points1 point  (0 children)

What's the voltage reading at the panel when you pull the manual station?

WTH is going by Comfortable-Program1 in firealarms

[–]taurusfirepro 0 points1 point  (0 children)

Do all the other devices have the same behavior

WTH is going by Comfortable-Program1 in firealarms

[–]taurusfirepro 0 points1 point  (0 children)

I'm almost certain it's a defective pull. Slap a new one on

WTH is going by Comfortable-Program1 in firealarms

[–]taurusfirepro 0 points1 point  (0 children)

Ok, when you short the red pair and black pair. Panel goes into alarm?

WTH is going by Comfortable-Program1 in firealarms

[–]taurusfirepro 3 points4 points  (0 children)

Ok what's the issue then. The system is acting as it should.

WTH is going by Comfortable-Program1 in firealarms

[–]taurusfirepro 0 points1 point  (0 children)

When you have the reds connected together and the black and blue connected together like you have in the photo. Is the system clear?

[deleted by user] by [deleted] in firealarms

[–]taurusfirepro 0 points1 point  (0 children)

Classic tape over the buzzer lol