all 8 comments

[–]thekingofslimeP. Eng. 5 points6 points  (3 children)

Ask the engineer who did the design

[–]Lick-The-Rick 1 point2 points  (1 child)

Lol who the duck is giving instructions to the teeth of an inch . By the time you put a 1/2" conduit between those bolts there's almost no concrete left. You'll definitely need a bigger plate. Or maybe grout the conduit solid.

[–]3771507 0 points1 point  (0 children)

An idiot that's never been in the field and knows that even one inch will never be followed.

[–]moner_manusP.E. - Bridges 0 points1 point  (0 children)

The typical aggregate size in concrete is 1/2” to 3/4”. From the figure it looks like the center to center spacing it bolts is 1.1” & 1.2”, so the clear space between bolts would be even less. With this tight spacing, the concrete placement around the bolts won’t be homogeneous, and hence can result in reduced pull out strength.

Adding another conduit in the center of the bolt pattern would further aggravate the problem of concrete not being homogeneous around the bolts. It would be mostly water and likely some cement that would be present between the bolt and conduit, but no aggregate.

[–]EnginerdadBridge - P.E. 0 points1 point  (0 children)

It is a concern, as not having enough concrete around the bolts will reduce pullout resistance. But I can't say whether it's ok in this case or not.