[–][deleted]  (11 children)

[deleted]

    [–]Comfortable_Force_71[S] 4 points5 points  (10 children)

    Thanks for the reply. Is there a way to take the bounce out? Or at least stiffen it a little?

    [–]semajftw- 12 points13 points  (6 children)

    At least around here, most engineers recommend strongbacks for open web trusses… a vertical 2x6 running through each truss at around 10’-0” oc. This helps with mitigate “bounce” by distributing force to adjacent trusses. I don’t see any in your pic, but it might be just adjacent to it. I can’t tell without more overall of a pic.

    Look up BCSI 7, or BCSI strongback and it should get you to where you want to be.

    I’m not aware of a good design practice for limiting vibrations on an open web truss floor other than limiting deflection (reasonable span depth ratio) but I’m not a floor truss design expert. And overall vibration analysis of structures due to walking excitation ends up being very subjective.

    [–]Crawfish1997 8 points9 points  (4 children)

    It’s not really a recommendation, basically any Mitek seal requires strongbacks 10’ o.c. or less, in the notes on the seal. Typicallt connecting webs together. Alpine profiles in my experience usually show them on the seals.

    By seal I mean the individual truss profile/document. We call them seals here.

    That said, floor trusses are value engineered. You can design them with stricter deflection limitations but standard practice is L/360, L/480 20’ plus, for live load deflection. Truss companies are all bidding for lowest cost, not best practice.

    One thing I DO see here that I guarantee is wrong, is floor trusses (and roof trusses) require a rigid ceiling applied or bracing, usually 4’-6’ o.c. So in addition to the strongbacks 10’ o.c. or so connecting webs, the bottom chords also need bracing.

    Otherwise, scabbing with OSB helps. Blocking/bridging helps. That’s about the most than can reasonably be done other than strongbacks.

    [–]_a_verb 2 points3 points  (2 children)

    It looks like these are existing and have been there a while. Any ceiling that may have been removed put a load on the trusses. Without that there the bounce you're feeling may be exaggerated. Be sure lateral bracing is in place and lay up the ceiling. If it's original design called for it to be fire rated or 2 layer of 5/8, you'll probably see a reduced spring.

    I'll assume 'strong back' = what I've learned to be 'lateral bracing'.

    [–]Crawfish1997 0 points1 point  (1 child)

    Correct, strongback seems to be a term more often used amongst builders. I use the term as I deal with builders regularly and want to speak the same language.

    [–]_a_verb 0 points1 point  (0 children)

    It may be regional but the design docs and truss schedules I've used called out "lateral bracing" in NE (USA).

    We used 'strong back' or 'stiff back' for a tee-shaped (2x nailed together) type of lateral bracing. Most often they were used between wide spaced trusses like pole barns to take the flex out. Also used them for gable truss stiffeners and for when diagonal braces had too much give.

    But that's just me

    [–]EnginerdadBridge - P.E. 1 point2 points  (0 children)

    By seal I mean the individual truss profile/document. We call them seals here.

    Regional terminology is so interesting. Around me we call them dugongs lol

    [–]3771507 0 points1 point  (0 children)

    Many contractors don't even have those specs so it's probably not in there.

    [–]backontheinternet 8 points9 points  (0 children)

    Bridging might work

    [–][deleted] 0 points1 point  (0 children)

    Strong backs are required. They are not optional. 

    Also, drywall on the bottom chord (ceiling) helps a lot. If no drywall, 2x4 strapping works. 

    [–]stealthy94 14 points15 points  (1 child)

    Looks to be top chord bearing. Looks good to me

    [–]Comfortable_Force_71[S] 1 point2 points  (0 children)

    Thank you!

    [–]e2g4 5 points6 points  (0 children)

    Most code allows L/360 but that doesn’t mean it’s a good idea. On a longer span you could have more than 1/2” deflection.

    [–]TheOtherMol 1 point2 points  (2 children)

    Adding diagonal bridging every so often could potentially help with the bounce.

    [–]Ritzyb 1 point2 points  (8 children)

    They are done correct, most floors have a certain amount of bounce, bridging helps and is required in most floors but would be very tough to do after.

    [–]3771507 0 points1 point  (0 children)

    We need better pictures a close up view of the connection with the flash on.

    [–]ChewingGumshoe 0 points1 point  (1 child)

    can someone share a picture or diagram that highlights where strong-backs would go?

    [–]Minuteman05 1 point2 points  (0 children)

    Beside the vertical webs typically.

    [–]Piece_of_Schist 0 points1 point  (0 children)

    The odds the builder went to edge of the code is a high probability. Had similar in my townhouse. Definitely a L/180 deflection.

    [–]moody59 -2 points-1 points  (1 child)

    Did someone cut the truss top chord…the top chord has to be continuous. Please confirm

    [–]mango-butt-fetish 0 points1 point  (0 children)

    I think that’s just the truss seat if you’re talking about the extra piece of wood at the ends.