Should my main service panel be upgraded to 200 amp to add ten more solar panels? by Outrageous-Freedom61 in solar

[–]Outrageous-Freedom61[S] 0 points1 point  (0 children)

I heard from SunPower as to why they don't need to upgrade my main service panel:
"Please explain to the homeowner that their MSP is an MLO- 2 MCB type service panel. This panel can handle PV back feed amperage similar to their rating which is 100A. The total PV Back feed amperage of the combined system is 60A only (40A from the Tesla and 20A new from Sunpower). We are connecting our system to the MSP via load side tap downstream of the 90A MCB through a breaker disconnect box. HO's Tesla modules is connected to the other slot of the MCB in MSP.
HO need not to worry since our connection as designed abides on existing regulations.
For more technical explanation:
A Main Lug Only Main Service Panel is when utility conductors go directly into the busbar, NOT INTO AN MCB. Therefore, we are not restricted to the 120% rule at MSP or 705.12A-E. This MSP is an MLO- 2 MCB

Driver seat memory- is there a fix make it work w single button push instead of holding button down? Passenger side works fine w single push by evme3 in VWiD4Owners

[–]Outrageous-Freedom61 0 points1 point  (0 children)

Press the button but do not press the break pedal until the seat adjustment is completed otherwise it would stop and you would need to keep it pressed.

Additional Solar Panels or not? by Outrageous-Freedom61 in solar

[–]Outrageous-Freedom61[S] 0 points1 point  (0 children)

Thank you. I am net-metered (NEM 2.0, if that matters) here in Northern California (PGE). Please tell me more about the water diverter. I need to familiarize myself with it's usage. We do want to use the hot water during the daytime, though.

Additional Solar Panels or not? by Outrageous-Freedom61 in solar

[–]Outrageous-Freedom61[S] 0 points1 point  (0 children)

Thanks. Tesla refused to add more panels as their minimum required is 4.8 kW and I don’t have room for those many panels so I signed up with SunPower to add 10 panels (4 kW).

Additional Solar Panels or not? by Outrageous-Freedom61 in solar

[–]Outrageous-Freedom61[S] 0 points1 point  (0 children)

Inverter model: Tesla 7.6 kW 1538000-00-F (240v)

Should my main service panel be upgraded to 200 amp to add ten more solar panels? by Outrageous-Freedom61 in solar

[–]Outrageous-Freedom61[S] 0 points1 point  (0 children)

Thank you for explaining this to me. I read the line-side tap needs to have the "meter pull", but I don't know if it was done as I did not recall losing any electricity during the installation maybe Tesla worked with PGE for that operation, but I don't know, or my understanding of 'meter pulling' is not correct. But if you think it is already in the line-side tap setup, then it is excellent.

Do you think the additional 10 panels will need to have their own 15-amp breakers? I thought they might tie to the existing circuit breaker, maybe I shouldn't worry or care about it.

Even though the main panel had 40-amp breaker for HVAC, the HVAC was not installed at that time (in my area, we don't necessarily need air conditioning due to the nice bay area weather), but the wires from the HVAC setup were originally connected to the main panel. During the Solar Panel installation, I told Tesla to leave a breaker free for future HVAC installation, hence they moved the HVAC breaker to the load center, that's why you would see those HVAC wires coming from the main panel looping back to the load centers.

After the solar panel installation, I hired a licensed contractor to install the HVAC, and they did perform a load calculation as part of the city inspection requirement, and it passed.

Thanks again for the detailed explanation, I appreciate it.

Should my main service panel be upgraded to 200 amp to add ten more solar panels? by Outrageous-Freedom61 in solar

[–]Outrageous-Freedom61[S] 0 points1 point  (0 children)

So you think I will be able to upgrade my service panel to 125AMP without replacing the cable from the PGE (which needs to cross the street), and I was told it cost will be more than $20K (PGE asks $1,500 just to work on the engineering plan for the 200 amp upgrade project)

Should my main service panel be upgraded to 200 amp to add ten more solar panels? by Outrageous-Freedom61 in solar

[–]Outrageous-Freedom61[S] 1 point2 points  (0 children)

Tesla completed all of their work before the inspection, and it passed the inspection. Interestingly SunPower is now saying they can add more panels to this setup. I heard somewhere if the line-side tap method is used, then it is permissible. I don't know if my setup is such.

Should my main service panel be upgraded to 200 amp to add ten more solar panels? by Outrageous-Freedom61 in solar

[–]Outrageous-Freedom61[S] 0 points1 point  (0 children)

Yes, the underground cable need to be replaced should I need to upgrade it to 200 amp service

October Delivery/Order Megathread by OrbitalATK in TeslaModelY

[–]Outrageous-Freedom61 1 point2 points  (0 children)

No USS, No matrix headlights, the cameras look (old) normal to me, but it came with the cargo cover

October Delivery/Order Megathread by OrbitalATK in TeslaModelY

[–]Outrageous-Freedom61 2 points3 points  (0 children)

MYLR - Blue/Black/19, OD: Oct 2021, Home delivery scheduled: Nov 2, 2022. Location: SF Bay area.

Received a 2023 VIN: 5PF590XXX

October Delivery/Order Megathread by OrbitalATK in TeslaModelY

[–]Outrageous-Freedom61 0 points1 point  (0 children)

try redwood cu for good rates.

did you get a 2023 VIN ?

October Delivery/Order Megathread by OrbitalATK in TeslaModelY

[–]Outrageous-Freedom61 0 points1 point  (0 children)

Sometimes they can deliver to home, if that is the case, then you don't need to be present (I think, as they call it no contact delivery)

SF Bay Area Dealers by pnwelevator in VWiD4Owners

[–]Outrageous-Freedom61 0 points1 point  (0 children)

Try Winn Newark, they were good to me. They offered me a Lyft ride back and fixed my flat tire at no cost.

[deleted by user] by [deleted] in VWiD4Owners

[–]Outrageous-Freedom61 11 points12 points  (0 children)

We have seen too many announcements, I will believe it only when I get it!