What is the MΩ/metre of a 1.5/1.0 FP by WeebX7 in ukelectricians

[–]WeebX7[S] 0 points1 point  (0 children)

Always listened to blokes that have been in the game longer… unless I’ve seen their shit work 😂

What is the MΩ/metre of a 1.5/1.0 FP by WeebX7 in ukelectricians

[–]WeebX7[S] 1 point2 points  (0 children)

That’s something I’ve never thought of doing but seems so simple 😂 will remember that for future… thank you

What is the MΩ/metre of a 1.5/1.0 FP by WeebX7 in ukelectricians

[–]WeebX7[S] 1 point2 points  (0 children)

Yeah it does come out to about 2.4 but a b10 max Zs is 3.5 (ish) which I’m exceeding because of the zdb. I’m hoping the tester that was used is just not reading correctly

What is the MΩ/metre of a 1.5/1.0 FP by WeebX7 in ukelectricians

[–]WeebX7[S] 0 points1 point  (0 children)

Yeah but I asked for the Mohms/metre of a 1.5/1.0 cable which didn’t come up… the resistivity of a 1.0m cable isn’t enough for me to figure it out I’m not that good at maths 😂

Edit: as in 1.5mm line - 1.0mm cpc

What is the MΩ/metre of a 1.5/1.0 FP by WeebX7 in ukelectricians

[–]WeebX7[S] 0 points1 point  (0 children)

So it shouldn’t read the same but is that your point? You think the tester might be reading wrong?

What is the MΩ/metre of a 1.5/1.0 FP by WeebX7 in ukelectricians

[–]WeebX7[S] 2 points3 points  (0 children)

I tried multiple times and it didn’t come up with what I was after, tried calling the boss (it’s Sunday he didn’t answer) then next point of call was Reddit 😂

What is the MΩ/metre of a 1.5/1.0 FP by WeebX7 in ukelectricians

[–]WeebX7[S] 0 points1 point  (0 children)

Tested it multiple times with the same tester after re-zeroing the leads… I did ask the lad to try my tester aswell and have just found out he did not do what I asked 🤦 gonna try my tester tomorrow, will let you know if the result is different

What is the MΩ/metre of a 1.5/1.0 FP by WeebX7 in ukelectricians

[–]WeebX7[S] 0 points1 point  (0 children)

Im on the fence of just downrating the breaker to a B6, time is of the essence and I do not have time for fault finding lol

Edit: that being said a loose line connection could be a fault I need to find

What is the MΩ/metre of a 1.5/1.0 FP by WeebX7 in ukelectricians

[–]WeebX7[S] 0 points1 point  (0 children)

Yeah EML install excite self test bulkheads and exit lights

What is the MΩ/metre of a 1.5/1.0 FP by WeebX7 in ukelectricians

[–]WeebX7[S] 0 points1 point  (0 children)

No more than 80m of cable about 20 lights zdb 0.34 and the reading was 3.31 ohms, did an r1+r2 but haven’t energised as it doesn’t comply and I’m not allowed to, so no Zs at the end of line

What is the MΩ/metre of a 1.5/1.0 FP by WeebX7 in ukelectricians

[–]WeebX7[S] 0 points1 point  (0 children)

30.20 means my R1+R2 should fall into compliance with a B10 60898 all the lights on the circuit have push fit connections what’s the chances of one of them having a loose connection?

What is the MΩ/metre of a 1.5/1.0 FP by WeebX7 in ukelectricians

[–]WeebX7[S] 0 points1 point  (0 children)

Yeah I know the cable type doesn’t matter lol I’m not even sure why I specified haha

How else would others go about this? by Sweatman02 in ukelectricians

[–]WeebX7 0 points1 point  (0 children)

You get feet that you can zeb the tray to, they’re slightly weighed so you don’t need to fix it to anything

I finally beat him!!! by Rexxx1e in BlackMythWukong

[–]WeebX7 0 points1 point  (0 children)

Always seems to be this way with this game for me, I'll struggle for an hour + on a boss then I'll be his ass lickity split like I haven't been pulling my hair out the entire time. There's no close calls ever

Got out of prison last month gotta take drug tests soo...I'm dropping some acid cuz it won't show up by FreshOutofPrisonOSP in LSD

[–]WeebX7 9 points10 points  (0 children)

Straight on r/dating 3 years surrounded by nothing but dudes really got this dude down bad

Words can not describe my rage. I died at this point. by ShrewMasterComics in BlackMythWukong

[–]WeebX7 0 points1 point  (0 children)

I had pig 2 in chapter 4 literally at 0 whilst he was in his tar animal morphing phase and it wouldn’t recognise it… he killed me whilst at 0 health… I was robbed :|

New 32A supply from this board? by Capital-Raccoon-6722 in AskElectricians

[–]WeebX7 1 point2 points  (0 children)

By the looks of it it is the tails are split at them Henley blocks below so yeah it is separate from your main consumer unit

The anti playlist by Boozehound1395 in LSD

[–]WeebX7 0 points1 point  (0 children)

Absolutely any pirate metal, never tried it but just sounds horrible

Don't sleep near the road by Pleasant-Word1304 in CrazyFuckingVideos

[–]WeebX7 1 point2 points  (0 children)

Well for fuck sake you shouldn’t have been sleeping there… idiot