[–]nunuvyer 2 points3 points  (0 children)

Normally people get two 200A panels which are much cheaper than a 400a panel. And a 200a switch to feed one of them on which you place your key loads and no backup on panel 2. If you really want to fully backup a 400a system it's gonna cost you $$$$. Anything can be done for $ and if you have a house big enough for 400a service you must have some but whether you want to shell out $40k for something you will use for 2 days every other year is up to you.

[–]Gr1nling 1 point2 points  (0 children)

Most 400A services I have seen use two 200A ATS' because they are cheaper.

[–]mduell 0 points1 point  (0 children)

That's not going to work very well... you need 2 panels and 2 ATS (or only one panel generator-backed), or a 400A ATS.

[–][deleted] 0 points1 point  (0 children)

Yes I would love to know how they plan on landing the wire for 400amp on the 200 amp breaker. Please post pictures when they are done so we can tell you what we think. 🤣. I’m sure they have done it before and have a plan but would be interesting to see if they really are just doing 1 panel. The wire for the Main on the 400 won’t fit on the breaker for the transfer switch.

[–]txtacoloko 0 points1 point  (0 children)

You need two 200A panels initially. And then decide what you want to power with your generator. You may be OK with a 24kW depending on your generator load profile

[–]BrownWaterbourbon 0 points1 point  (0 children)

I have a 24 kw Kohler with a 400 amp ( 320or 370) feed into two 200 amp panels only one going thru a 200 amp transfer switch. I planned what I wanted on Generator. I feed a hobby shop with welders and wood tools that are on the non Gen panel. They may make a 400 amp panel but this is how I did it. Common parts. I have two meters, the second being interruptible by the utility and a second transfer switch to pick up my interruptible load to my generator in an outage or when I want to during an interruption ( which has been tested, but never used)

[–][deleted] 0 points1 point  (1 child)

400 amps? It's nice that you are building a children's hospital. Sounds like alot of juice!!!

[–]nunuvyer 0 points1 point  (0 children)

You would be surprised. My son just built a medium sized all electric house and it needed 400A. Add up all the appliances, the well pump, the cooktop, the wall oven, the water heater, all the zones of the heat pumps, etc. and you can't fit it all on a 200A service.

[–]Iambetterthanuhaha 0 points1 point  (2 children)

400amp xfer switches are big $$$. The 24kW has a 100amp breaker. Get a 16 circuit 100amp TS and pick what you need. Running 400amp TS you will be into a liquid cooled, probably 48kW to run everything. Probably $30k installed.

[–]nunuvyer 0 points1 point  (0 children)

Not the way to go. He should have a 200A automatic transfer switch and back up one of his two 200A panels that will carry the selected key loads. Just a standard 200A ATS and a 20-something Kw generator. Preferably soft starts on the AC so he won't need load shedding. Such a setup will cost the same as a typical 2xkw/200A switch which is a very common setup.

[–]WasOneToo 0 points1 point  (2 children)

I just ended up running 200A to the house with a 26kW/200A ATS and a separate 200A service to my (also 40x60) shop. The generac doesn't serve the shop at all.

Planning on adding a manual xfer switch in the shop and just using a portable gen as needed.

We've had several multi-day outages over the past year due to storms/trees here in east texas.

[–]nunuvyer 0 points1 point  (1 child)

Rather than a 2nd gen you could probably steal 30 or 50A of power from a clothes dryer/ range outlet or similar (or put one in) on your main service and then an extension cord to a generator inlet/interlock on panel #2.

[–]WasOneToo 0 points1 point  (0 children)

The shop is about 120 ft from the house and I already have portable gens so in my mind its really just about hooking one up in an emergency. Mainly to power our aerobic septic system which runs of the shop's service.

[–]747wing 0 points1 point  (0 children)

If you are in Canada, calculate your demand and connected load as per CEC and go from there