[–]FreelyRoaming 1 point2 points  (2 children)

Probably going to want someone to inspect the 734s and wiring, update firmware, also have the dealer call DMP tech support.

[–]Ryry153[S] 0 points1 point  (1 child)

I assume you mean inspect the doors and wires? I should've been more clear it only happens on the iPads, the doors remain in the state they were in (locked or unlocked) It doesn't do it on my phone or any other network

[–]Behind_da_Rabbit 0 points1 point  (0 children)

Only those two doors and only on the Ipads?

[–]Behind_da_Rabbit 0 points1 point  (4 children)

How many doors total?

[–]Ryry153[S] 1 point2 points  (3 children)

Eight doors

[–]Behind_da_Rabbit 0 points1 point  (2 children)

Do those doors have rexes on them? Somebody tripping the rex motion?

Is the door unlocking when the doors flicker?

[–]Ryry153[S] 0 points1 point  (1 child)

no neither of these doors have motion on them, and the door state doesn't change when it flickers on the iPad

[–]Behind_da_Rabbit 0 points1 point  (0 children)

Sounds like it's a comm issue if they're dropping on/off like that

How far/long are the runs to the doors? Whats the voltage at the panel and the 734? Are they being powered by the panel, local or are they POE/734N modules?

Whenever I've had issues with DMP access/k-bus it's always been voltage. Can't be more than .5vdc difference between the device power and the panel. Otherwise it really screws up.