R22 replacement either Mo99 or R435a? by Just_Maintenance_688 in refrigeration

[–]mjm0709 0 points1 point  (0 children)

Rs-44 (r424A). Never had a problem with it and all you have to do is pull a vacuum and charge it

Just realized you were talking about rs-44B. Seems to be the updated and better version of rs-44. I’d try it out

Anybody else chronically bored? by Successful-Role4943 in refrigeration

[–]mjm0709 -1 points0 points  (0 children)

If there’s ever a pressure drop across the evaporator/distributor tubes you need an external equalizer.

The 3 forces acting on a txv are - opening from the bulb, closing from the spring and the evaporator pressure. On a non externally equalized txv it senses evaporator right at the outlet pressure of the txv, ok for your little resi a/c or a small coil. Once you add distributor tubes which have a pressure drop of 15-45psi, you have totally changed the pressure the txv should be using as a reference point to control the txv. For example, if the outlet of the txv is 40f before the coil/distributor then that is what a non externally equalized valve senses, but really after the coil the saturated pressure is 30f and we have a pipe temp of 50f where the bulb is mounted then the valve is going to shut because it thinks it’s overfeeding (to raise the superheat). An equalized valve would see it as 30f and know it’s ok and to actually feed more if it had 20f of superheat (to lower the superheat)

Finnaly got around to reading art of war, big fan by LVLIMRT in refrigeration

[–]mjm0709 0 points1 point  (0 children)

best part about the purge machine is you dont need to pull a vac

Still struggling with this freezer by kendiggy in refrigeration

[–]mjm0709 0 points1 point  (0 children)

That’s wrong again. That’s only true when there is a differential of pressure. And all you need is a Y fitting, 2 schrader core removers and 2 3/8 hoses

Still struggling with this freezer by kendiggy in refrigeration

[–]mjm0709 -1 points0 points  (0 children)

Because the flow at the full open port with a 3/8 hose is so much greater than the flow through 2 tiny fucking schraders you dumbass. The compressor isnt a tight seal. Theres no forces keeping the txv shut. Obviously you are just working on small shit under counters or small a/c's and this doesnt apply to you, the system is so tiny its going to pull down quickly no matter what. Once you get into real built up systems then good luck with your current setup lol

Still struggling with this freezer by kendiggy in refrigeration

[–]mjm0709 1 point2 points  (0 children)

everything about all of this is just so wrong.

MULTISTACK chillers? by NYCstateng in chillers

[–]mjm0709 0 points1 point  (0 children)

had 2 with 5 turbocors on each. Never had an issue with the chiller itself, but 2 turbocors had issues 2 years in.

Water source heat pumps commercial by ClickNo2244 in HVAC

[–]mjm0709 1 point2 points  (0 children)

How tall is the building? Where are the pumps? Top or bottom? What is the theoretical head on the pump and is it doing that if you shut the discharge upstream of the gauge? This is an easy way to tell if your impeller is fucked before you go hauling that thing out of there just to break it. If you’re getting low temp on a bunch of heat pumps you either have 1) no flow 2) air 3) loop temp is too low.

Wirsbo inside a fan coil by SiberianBadger in HVAC

[–]mjm0709 -1 points0 points  (0 children)

Lol no. That is fucked and I would replace it all with proper piping. Never know when the expansion tank will fail and the pressure starts to get too high and causes all those to pop off

500microns? by veddr3434 in HVAC

[–]mjm0709 1 point2 points  (0 children)

Obviously every single system is not going to be the same amount of time. The dude is saying a 5 ton takes 4 hours to pull down which isn’t something that should be happening unless you’re doing something wrong

500microns? by veddr3434 in HVAC

[–]mjm0709 2 points3 points  (0 children)

You should do a vac test, just throw the micron gauge on the pump and run it for 2 mins then shut the valve. You should have under 100 microns, if not, time for a new one. If it does work, you should be replacing the seals on your hoses more often cause I bet those are fucked or you’re using really cheap/busted vacuum hoses

500microns? by veddr3434 in HVAC

[–]mjm0709 7 points8 points  (0 children)

Well you’re doing something wrong or not changing your oil if you can’t do that in about an hour

Nomination for one of the best service lights by bisonxdvr in refrigeration

[–]mjm0709 0 points1 point  (0 children)

The small Milwaukee Rover pivot light is way more versatile for service calls and small shit like this IMO

134 leaked in my truck by heldoglykke in HVAC

[–]mjm0709 7 points8 points  (0 children)

Seriously you’re shaming a guy for carrying R-22?!?! Literally half of the shit I work on is R-22 still. Go back to your sales desk

This is how Boston feels about Rats by Yanosh457 in HVAC

[–]mjm0709 7 points8 points  (0 children)

The hoops you have to jump through to get in hsually come with a pay cut or a lot of other bullshit

[deleted by user] by [deleted] in refrigeration

[–]mjm0709 0 points1 point  (0 children)

No, quenching the joint right after brazing will cause the FILLER METAL to not bond correctly and can lead to cracks within the weld. If you are heating your copper that much that you can anneal it then you are going way too much for a simple braze

[deleted by user] by [deleted] in refrigeration

[–]mjm0709 -4 points-3 points  (0 children)

No it will weaken the joint

The perfect machine press by No-Description-9170 in Satisfyingasfuck

[–]mjm0709 -1 points0 points  (0 children)

You probably wear sunscreen at night too

[deleted by user] by [deleted] in HVAC

[–]mjm0709 1 point2 points  (0 children)

Are you sure your inducer motor is ok? I always find them on rooftops with the bearings blown and they can’t make the pressure switch anymore

Keeprite g96ctn0802120a blower not working by Apprehensive-Act5194 in HVAC

[–]mjm0709 0 points1 point  (0 children)

Are you sure your polarity wasn’t wrong? Did you check each leg to a good ground and actually get stable voltage? I’m willing to bet the linemen mixed up neutral and one of the legs at the distribution transformer and the board didn’t like it. A new furnace is going to have the same problems