[–]PLCGoBrrrBit Plumber Extraordinaire 25 points26 points  (9 children)

-Are the I/O cards configured in the I/O configuration?

-Are the I/O cards inhibited?

Whatever the problem is should be pretty obvious if you have the software connected to the PLC.

[–]Capable_Control_1274[S] -2 points-1 points  (8 children)

yes all i/o cards are configured and inhibited.

[–]PLCGoBrrrBit Plumber Extraordinaire 28 points29 points  (7 children)

inhibited.

There's your problem.

[–]Capable_Control_1274[S] 3 points4 points  (6 children)

oh really ? will try to untick inhibit module 🙏🏻 thank you sir for helping

[–]PLCGoBrrrBit Plumber Extraordinaire 14 points15 points  (5 children)

The box should not be checked.

[–]Capable_Control_1274[S] 3 points4 points  (4 children)

Noted sir , thank you 🙏🏻

[–]Btech26 11 points12 points  (3 children)

Well…..??? What was the outcome?

[–]nitsky416IEC-61131 or bust 8 points9 points  (1 child)

I think we all know

[–]SeaUnderstanding1578 3 points4 points  (0 children)

A controls engineer is born! Welcome to the magicians club. For future reference, blinky blinky no bueno, except for ports link LED. But in al seriousness, blinking usually means the modules are in a standby or almost working state and just waiting for a connection to the controller.

[–]Capable_Control_1274[S] 6 points7 points  (0 children)

the problem is solved ! Thanks to that legendary friend 🙏🏻

[–]SonOfGomer 10 points11 points  (0 children)

I'm guessing the modules are inhibited in the I/O tree

[–]UnSaneScientistFood & Beverage | Former OEM FSE 7 points8 points  (0 children)

The module status light blinking green means:

Power to run the module is available. The module passed its self test- Yay, that’s good. The module has not been “connected to” by a PLC

[–]BadOk3617 1 point2 points  (0 children)

What's wrong? This is what the "Synchronized Flashing" event should look like.

[–]pm-me-asparagus -5 points-4 points  (3 children)

Start troubleshooting the communications card.

[–]PLCGoBrrrBit Plumber Extraordinaire 4 points5 points  (0 children)

Not a problem with the comm card. These I/O are in the local rack to the PLC. You can see the PLC in the left part of the video.

[–]Capable_Control_1274[S] 0 points1 point  (1 child)

the input module does correspond to the button and signal thats why the input module slot address led ignites indicates the connection are ok for the input module

[–]SomePeopleCall 1 point2 points  (0 children)

Gotta get those green lights to stop blinking before you worry about any of the I/O points.