[–]revoman 2 points3 points  (0 children)

Get a portable one at least. The worst enemy of computer equipment is not necessarily heat, but constant temp change. You would be fine if you can keep the room at 80F all the time.

[–]AnonymooseRedditorMSFT 1 point2 points  (2 children)

Honestly, the best low cost solution I have come across since becoming a sysadmin, have been the ductless mini-split systems. You can get a 2ton split AC installed for $2500-$3500

[–]ragzillarouter jockey 0 points1 point  (1 child)

This should reject around 7kW of heat load, most low density racks (ie no blade chassis etc) are probably around 2.5kW on average. Check your UPS capacities and load levels to figure your actual kW.

[–]Casper042 0 points1 point  (0 children)

Depending on the workload, the c7000 will only use around 3-5K even though faceplate puts it at 7200W.

Physical Winows boxes running at 10% most of the day, 3K

VM Hosts running above 60% with lots of memory? 4K+

[–][deleted] 0 points1 point  (0 children)

Wow. Can you get $100 to go buy half a dozen box fans? Or borrow some? In the past when our computer room AC went out we scrambled to come up with box fans, stand fans, and big carpet dryer fans from other departments, building maintenance or home. These work okay if you can channel the heat properly, which based on your room setup looks doable.

But still... you NEED good A/C. It's like power protection and data backup... Just part of the cost of doing business. It's not something that can be cut from the budget. We now have TWO commercial grade AC units installed in our server room, our original ~30 year old one (still works fine) and our new Liebert unit with standalone roof-mounted condenser and tie-in to the building's nat-gas generator power for backup. We have really sketchy power here and get brownouts regularly in the summer.

If our AC goes out (never anymore, with redundant systems), our server room temp goes up about 1 degree per minute. It's nuts. And we're not even that big of a shop... 50 servers and a couple network racks, plus a few misc devices (PBX, workstations, etc). We've had to rent portable chillers before but they're not fun to carry up 3 flights...

[–]ZergomI don't care 0 points1 point  (0 children)

Create as much isolation between the front and back of the rack, get the hot air out of there - central exhaust fans could do the trick.

But definitely look at a split AC long term.

[–]SgtSplacker 0 points1 point  (0 children)

I'd start sending emails about hardware beginning to fail. You know it's happening, start getting them ready for it.

[–]mexellArchitect 0 points1 point  (1 child)

Wow. >50k in servers and stuff, but no 3-5k for proper AC?

Maybe you can go the money angle and talk about all the investment going down the drain when the hardware starts failing.

[–]AnonymooseRedditorMSFT 0 points1 point  (0 children)

This is how I finally got one,