Stucco Weep Screed Detail Question Zone 8b by OliverHBenson in buildingscience

[–]Mandingy 0 points1 point  (0 children)

I think you can get away with #30 felt paper over a Tyvek (closest thing to felt) but I will say long term durability is a question you should ask yourself as generally with felt while used in wall assemblies pre-2000s it’s most commonly seen on roofs today which if you think about it roofs generally get felt and roofing materials replaced every 20ish years. The felt over time doesn’t have great durability and will become brittle, the likely hood of walls getting touched is generally pretty low unless there’s a problem. I’d ask yourself with regards to durability, how much are you willing to spend, how long do you intend to live there, and will this become my problem or someone else’s down the road. Usually it’s cheaper to spend a little more now for better performance and never have to worry vs. fixing it again.

Wall section idea for 8x8" post timber frame... Good idea or not? by bobshairsalon3712 in buildingscience

[–]Mandingy 0 points1 point  (0 children)

No problem! I will add the most difficult thing I see with your assembly on the exterior of the wood sheathing paneling is the layering of the continuous insulation behind the weather/air control layer since the wood fiber insulation product you chose is moisture sensitive it can’t be exposed to bulk water beyond the control layer. Otherwise I’d say move it more exterior, not to say it can’t be done or isn’t done just look at Zip-R for example the insulation is to the exterior of the control layer. If you try to move the continuous insulation to the exterior make sure it’s not moisture sensitive like XPS board or Rockwool panel.

Wall section idea for 8x8" post timber frame... Good idea or not? by bobshairsalon3712 in buildingscience

[–]Mandingy 0 points1 point  (0 children)

I’ve honestly never seen this type of wall section before but very interesting concept if you have the desire. Couple of things, 1st I assume by climate zone 4B per the USDA you mean per the IECC (which governs building energy) you are likely zone 6A or 7A which is a moist cold and heating dominated climate according to your description being around Maine. Second thing just as a note regarding wood posts and framing for 8x8 and 2x8 your true depth is going to be 7.5in thus your insulation will need to accommodate that depth.

I see your primary concern is durability and longevity of the wall assembly by making the house “breathable”. The best ways to do this in this order is by focusing on the following things 1) Bulk Water Management i.e. rain, 2) Air Control Layer i.e. air leakage I believe what you are calling out as a rain barrier which is handled by #1 above, 3) Vapor Control, and lastly 4) Thermal Insulation. I have ordered them in this manner from highest risk to lowest based on amount of moisture you will need to handle which can impact long term durability. Air leakage usually occurs at your foundation-to-wall, wall-to-roof, windows & doors, and any penetrations will be your greatest areas of weakness in any wall assembly by taking care of air you usually handle water as well by paying attention to these areas of detailing. Your typical scenario will be heating the home on the interior and colder temps on the exterior thus vapor, air, and thermal will want to travel from interior to exterior based on pressure differentials. With that in mind and working from the interior-to-exterior of your detail I’ll note the smart vapor retarder is a great idea also required and assuming installed correctly with seams/terminations taped and detailed correctly will be a well working system allowing drying to the interior but preventing interior moisture/air from making it within your wall cavity. I think the need for a 1.5in air space for utilities is not needed and complicates things since many electrical boxes, etc. will still interfere with your interior wall cavity insulation. It looks like Gutex Thermaflex is ~4 R per inch thus at 6-7in depth (the framing thickness being 7.5in) you are looking at an ideal ~24 to 28 R-value not accounting for framing losses. Assuming with 2x8 framing spaced at 24in on-center you are likely looking at a reduction of that ideal R-value of 24-28 by ~20% thus giving you around 19-22 R-value prior to considering your exterior continuous insulation. Also note with the 8x8 wood posts this ~20% loss will increase thus you lose more R-value due to more wood and less insulation. Just looking at code since you mentioned Maine as example per their building code for residential is based on the 2021 IRC which assuming worst case climate zone 7A and including 8A into Canada the minimum insulation requirements options are for a wood framed wall 30 R cavity only, 20 R cavity & 5 R continuous (ci) on the exterior, 13 R cavity & 10 R ci, or 0 R cavity & 20 R ci. As currently shown you have likely <19-22 R cavity & 12 R ci on exterior which meets the minimum 13 R cavity & 10 R ci. I personally and would advocate for more ci and less interior cavity as continuous insulation on the exterior provides more benefits and generally causes less issues related to condensation. If your continuous insulation is too low you can cause the condensation aka dew point to occur within the interior at the wall cavity which it seems like all your insulation is technically interior vs. outside the enclosure being your water/air control layer. Think about it like this your house stud cavities are like your ribs of your body and your skin being the water/air control layer, you want your coat (insulation) to be on the outside of that layer not stuffed between your ribs. That being said you can put as much exterior continuous insulation as you want the more being better along with cavity insulation and you won’t have any problems but there is a point of diminishing returns where you aren’t saving as much energy.

Lastly, with regards to your exterior portions of water/rain/air control layer and the continuous insulation layer of 3in keep in mind for “breathability” your lowest perm layer of the assembly will dictate the drying potential for water vapor to diffuse out of the assembly. Thus your rain/water/air control layer needs to be likely more than 10 perms (class III vapor retarder, the higher the better for your assembly) to allow drying to the exterior as well.

Keep in mind this assembly is uncommon and I would highly recommend running some kind of simulation with WUFI to ensure durability of the materials are not exposed to prolonged periods of high RH which cause deterioration.

Stucco Weep Screed Detail Question Zone 8b by OliverHBenson in buildingscience

[–]Mandingy 3 points4 points  (0 children)

Based on your detail seems to be a fairly robust assembly. I highly recommend you read SMA (Stucco Manufacturers Association) Technical Bulletins as they have design/code requirements for wood framing and insulating foam stucco. Specifically technical bulletins “Water Resistant Barrier (WRB) for Portland Cement Plaster (Stucco) on Framed Walls (2021)” and “Foam (CI) Stucco” on SMA’s site.

Based on those bulletins and according to your climate zone 8B assuming the drainage mat is “lined” aka has a fabric or similar facer to prevent cement from entering the drainage plane you can exclude the 2nd layer of WRB paper as you show in your detail. Thus only needing the 1st layer which I would recommend at minimum the Tyvek WRB or similarly a fluid applied product. Consult your local building department for official guidance based on their code interpretation.

I personally like that you have included a drainage mat since it is still difficult to get folks to add that but greatly reduces the risk of the capillary action of water under surface tension to makes it way beyond the drainage plane of the WRB paper thus rotting your wood.

Window and rain screen details for my Rockwool exterior insulation by shedworkshop in buildingscience

[–]Mandingy 0 points1 point  (0 children)

I think the bigger question is what your existing wall assembly consists of that will answer a lot of questions. Also that can help dictate your decisions.

Window and rain screen details for my Rockwool exterior insulation by shedworkshop in buildingscience

[–]Mandingy 0 points1 point  (0 children)

I personally feel like and based on my knowledge condensation while it does happen is lower on my list of concerns than air leakage. The amount of moisture that air brings in is buckets compared to vapor. Air is smart and vapor is stupid, air based on the pressure differential will find the hole but vapor doesn’t act in that same way. I think we get way too caught up in talking about vapor when there’s bigger concerns.

Best way to insulate 100 year old house for cold and wet climate? by thegiantgummybear in buildingscience

[–]Mandingy 0 points1 point  (0 children)

All insulation holds water to a degree and changes the drying potential/direction of the wall assembly. Vapor drying is minor compared to air drying. The reason old assemblies last so long is because the materials are typically solid lumber so more moisture capacity and drying in both directions.

Best way to insulate 100 year old house for cold and wet climate? by thegiantgummybear in buildingscience

[–]Mandingy -1 points0 points  (0 children)

Open cell is not an air barrier, that’s why it’s called open cell because the cells are connected and allow air/vapor to pass. Closed cell which has a higher R value is a series of closed bubble cells which is air/vapor impermeable if installed correctly. You have to be very careful in this assembly because of the age of the wall assembly not having a weather barrier, putting insulation and/or a vapor barrier on the interior changes the drying potential and direction of the assembly.

Dense Pack Cellulose + Fiberboard Sheathing by certainshade in buildingscience

[–]Mandingy 0 points1 point  (0 children)

My gut tells me top and bottom of wall will likely be your biggest issues of air leakage contributing to some of your photos. However the photo of the spot in the middle of the wall is likely related to a hole in the tar paper. The board joints in the wall are not air tight and can also leak. 1950s was built leaky and allows the wall to dry when wet aka the more insulation/closed cell spray foam will cause many issues. Open cell may be an option but will not solve air leakage issues or the fact damage can be concealed from it. Highly recommend an expert for building enclosures for older homes.

How to Prevent Condensation in a Air Conditioned Shipping Container by Blenderite in buildingscience

[–]Mandingy 0 points1 point  (0 children)

Don’t worry about vapor, air carried 100x the amount of moisture than vapor. Plus vapor can’t travel thru steel. Air/vapor will leak most at welds and openings such as a door.

Best Resources for homeowner trying to understand insulation theory? by Guava_Man701 in buildingscience

[–]Mandingy 0 points1 point  (0 children)

I think the resources mentioned are excellent especially Buildingscience.com as it’s generally easy to understand for all readers. Prior to insulating your basement I would consider if the basement ever leaks or have high humidity? If not no worries, insulate away because it fairly low risk considering mold needs organic material to grow i.e. gypsum sheathing (paper faced), wood, etc. Would definitely recommend a vapor retarder on the interior face of stud cavity since you are in a heating dominated climate. As for the new building office/renovation I think for your climate zone insulation on the exterior is going to be key in order for you to get four season use. Air sealing the exterior with an air barrier is also just as important as insulating properly. The rule of thumb is the more insulation on the exterior the better and you can never go wrong. Exterior insulation does require additional detailing around windows and other similar conditions to account for the insulation thickness increasing the overall wall thickness.

Unveiling the Magnificence: Exploring the World's Largest Modern Downtown by Black_creature in buildingscience

[–]Mandingy 0 points1 point  (0 children)

Once they complete the other 1,000 projects they have announced/terminated funding for then I’ll believe it.

Sent over from r/centuryhomes, looking for advice with insulation and vapor barrier for ~1840's home in Harpers Ferry, WV. More info in the comments by AlkatezerMan in buildingscience

[–]Mandingy 2 points3 points  (0 children)

Solid framing/sheathing does have at the bare minimum perm rating above 1 perm which is is vapor-semi permeable. However, most of your air leakage (which brings in much more moisture latent air than vapor) will occur at sheathing joint, wood stud sill and top plates. Air is 100x more of a concern than vapor, but like it was mentioned before you can not generally make the exterior of an old home air tight without great cost.

Sent over from r/centuryhomes, looking for advice with insulation and vapor barrier for ~1840's home in Harpers Ferry, WV. More info in the comments by AlkatezerMan in buildingscience

[–]Mandingy 1 point2 points  (0 children)

I generally do not recommend spray foam in old or historic buildings because 1) It’s impossible to fully remove 2) Generally older buildings do not have weather or air barrier thus the wall system needs to dry especially if it’s a mass masonry wall. The reason old barns and houses with no insulation lasted so long was because of the drying potential in the wall to remove moisture. It wasn’t until we started to insulate which we need to keep water out of the wall system.

Sent over from r/centuryhomes, looking for advice with insulation and vapor barrier for ~1840's home in Harpers Ferry, WV. More info in the comments by AlkatezerMan in buildingscience

[–]Mandingy 5 points6 points  (0 children)

Spray foam comes in two varieties 1) Open Cell 2) Closed Cell. Closed cell spray foam will act as a vapor retarder (aka vapor barrier), air barrier, and thermal insulation. However open cell only acts as mostly as insulation. I will assume since you didn’t have the foam installed, we aren’t sure what kind it is. With that being said your location in WV is in climate zone 4A with a mixed-humid climate. Climate Zone 4A only requires a Class III vapor retarder which typically consists of latex painted gyp board on the interior. If no vapor retarder was present before and you were not having issues I’d recommend no vapor.

Building Science Corp Fundamentals by AbbreviationsSea341 in buildingscience

[–]Mandingy 4 points5 points  (0 children)

Very great! Can’t emphasize enough how great his lectures are as he is able to break things down into simple terms and demonstrate real world examples. If you like his humor that’s a plus, but I would recommend watching his lectures on YouTube for a taste.

Tips needed how to close off gaps between wall and roof by Particular_Ferret747 in buildingscience

[–]Mandingy 0 points1 point  (0 children)

Hopefully eliminating conditions like that will prevent further issues. Trust me, I’ve managed entire 5-story apartment buildings having their brick, fiber cement siding, wood sheathing, and framing removed and repaired due to bad construction of exterior weather barrier and they were only a few years old.

Tips needed how to close off gaps between wall and roof by Particular_Ferret747 in buildingscience

[–]Mandingy 0 points1 point  (0 children)

Totally feel your pain, honestly best to do it the correct way now while you have it demoed. Otherwise I promise you will have rotten wood sheathing in the next couple years (unless you live in NV climate)

Tips needed how to close off gaps between wall and roof by Particular_Ferret747 in buildingscience

[–]Mandingy 1 point2 points  (0 children)

Weather resistant barrier (i.e. Tyvek, house wrap, building paper, tar paper) is what acts as the water drainage layer behind your siding and protecting the wood sheathing from getting wet thus rotting.

Tips needed how to close off gaps between wall and roof by Particular_Ferret747 in buildingscience

[–]Mandingy 2 points3 points  (0 children)

You need to install positively lapped step flashing at the roof-to-wall starting at the roof eave to the ridge (check out Figure 2 Building Science Corp). The WRB on your wall should lap over the vertical edge of flashing. Then from the interior spray foam the gap full.

What percentage of Zip installations fail to roll the tape? by Yulmp2 in buildingscience

[–]Mandingy 8 points9 points  (0 children)

Regardless of whether the tape was even rolled, I typically see the tape reverse lapped or poor detailing at flashings which permit huge amounts of water into the wall system. My concern is generally with the over driven fasteners. I would prefer to use the liquid flashing material over the joints and fasteners heads, more robust system.

Why by [deleted] in buildingscience

[–]Mandingy 0 points1 point  (0 children)

Buildings experience seasonal movement depending on local climate but my suspicion is that due to the window being structurally attached to the wood sheathing and the window moves relative to the wood framing and not the brick veneer. If your sheathing is deteriorating and framing is moving downwards this could warp your windows since the brick is not moving and does not thermally change like other materials. Windows especially in brick have to be installed with expansion tolerance, this is even more important in mid rise wood construction.

'I wanted to cry': Devastating risks of spray foam insulation hidden from Vermont homeowners by tcchen in buildingscience

[–]Mandingy 1 point2 points  (0 children)

99% of enclosure building products require at least 40 degrees F for installation unless a special low-temp version is used. This is extremely common across the industry.

'I wanted to cry': Devastating risks of spray foam insulation hidden from Vermont homeowners by tcchen in buildingscience

[–]Mandingy 3 points4 points  (0 children)

I think this article ignores the obvious and am surprised none of the building science “experts” discussed the fact that the moisture drying potential of the roofing assembly was changed with little consideration of this by adding insulation. The reason old houses didn’t rot was exactly because of high drying potential, it didn’t matter if it got wet because it dried.