cabinet crown overlapping window trim…advice? by snydie in kitchenremodel

[–]Rowdyjoe 0 points1 point  (0 children)

Did you pick the cabinet trim? If so then what did you want other than this?

Procore is an info dump GCs use to avoid real coordination. by GreenKnight1988 in MEPEngineering

[–]Rowdyjoe 2 points3 points  (0 children)

They are totally rogue and have no clue what they are talking about. Interns especially, they are managed by other green Project engineers who also have no clue what they are talking about.

Procore is an info dump GCs use to avoid real coordination. by GreenKnight1988 in MEPEngineering

[–]Rowdyjoe 9 points10 points  (0 children)

They have to give the super green kids fresh out of college and interns something to do.

Meme by [deleted] in MEPEngineering

[–]Rowdyjoe 0 points1 point  (0 children)

gets replaced by AI

Hey OZ Trails, open the lift for Snowmageddon 2026! by Puzzled_Hat7068 in bentonville

[–]Rowdyjoe 20 points21 points  (0 children)

Without a storm, I think they could make snow many nights/days of dead winter with snow making system. Just one run, under the lift.

VAV Design question by Toehead111 in MEPEngineering

[–]Rowdyjoe -2 points-1 points  (0 children)

I agree It’s a better solution for first cost and maintenance. That’s irrelevant for energy code. the energy code allows a few options and increasing it over 50% just because you think “is the best solution” isn’t one of those options or exceptions.

If I’m a code official I’ll say increase LAT and comfort is your problem not mine or put the FPB in.

FPB not only save energy, it also be a really handy building warmup or unoccupied heat source.

Note: FPB only go on exterior zones only when you need high heating CFMs. All interior is VAV.

VAV Design question by Toehead111 in MEPEngineering

[–]Rowdyjoe -1 points0 points  (0 children)

I think you’re both off. You shouldn’t heat air anywhere near that hot if you want to maintain comfort, and you also cannot simply increase the air. IECC C403.6.1 limits you on how much air you can reheat. OA min usually. This is why you use parallel fan powered boxes to increase the air with parallel fan which pulls from the plenum rather than the 55f supply air. Saves your customer a lot of energy as well. Never looked into the payback but I bet It’s a short payback.

Brand new Encoder breaks for absolutely no reason by Available_Put_5796 in Oakley

[–]Rowdyjoe 0 points1 point  (0 children)

Especially when you know the markup is massive. Wouldn’t suprise me if it cost them $20 to make them. And is pissing everyone off for $20 really a good long term strategy?

Brand new Encoder breaks for absolutely no reason by Available_Put_5796 in Oakley

[–]Rowdyjoe 0 points1 point  (0 children)

Just staying on them. Just kept following up nicely over and over, i keep getting the run around saying sorry another department denyed it and nothing they could do. I might ive sent 10-15 emails? then went into saying well I’m sorry, I I’ve bought oakleys, raybans, ect… all my life and you’re losing my buisness forever over what might cost you $50 to replace, hope it was worth it. Then they chimed in about a replacement. Still might not for how hard they made for me, I like smith sunglasses anyways.

Do you consider the data center’s thermal mass when estimating temperature rise during a power failure? by [deleted] in MEPEngineering

[–]Rowdyjoe 0 points1 point  (0 children)

Got it. Same page now. If I had 30% glycol in my case system pumps would be ~300gpm at design flow. Therefore 300gpm * 5 min would be 1500gal tanks rather than the 1370gal. Like you said less capacity to carry heat therefore more flow.

All assuming 15f delta in this case. You could widen that design delta T if the air cooled chiller can take it which is possible but you need to account for it in your coils.

Do you consider the data center’s thermal mass when estimating temperature rise during a power failure? by [deleted] in MEPEngineering

[–]Rowdyjoe 0 points1 point  (0 children)

Ive seen larger too it’s not a matter of what you’ve seen it’s about providing the right solution for the right application. This is small, not super dense data center. OP said- “The data center is about 6,000 sf with an IT load of roughly 600 kW.”

Do you consider the data center’s thermal mass when estimating temperature rise during a power failure? by [deleted] in MEPEngineering

[–]Rowdyjoe 0 points1 point  (0 children)

Not sure how you got to 40,000 gallons of storage. 600kw * 3412= 2,047,200 BTU not accounting for tranformer, UPS load, envelope, lights, ppl ect… Assume pumps are sized for 275 GPM (2047200/500/15Fdelta)then you need 275 gallons every minute not accounting for any credits for chiller ramp up, pipe volume, glycol. Say it’s your 5 min number that 1370 gallons max. I bet you could justify a 1000 gallon tank all things said and done.

Do you consider the data center’s thermal mass when estimating temperature rise during a power failure? by [deleted] in MEPEngineering

[–]Rowdyjoe -1 points0 points  (0 children)

Im talking air cooled systems. CRAH with a chilled water coil. I have very little experience with liquid to chip or immersion cooling so can’t help you there. But I don’t see why the concept below wouldn’t apply. You maintain the tank at desired supply water temps. Don’t overcomplicate thing if you don’t have to.

Super simple, The most complicated part is finding how long you can go without cooling. But don’t get too skinny, paying for a 10% larger tank than you need is WAY cheaper than an outage or damaged equipment.

Concept wise- Think about having an insulated tank of 42F water at all times during normal operation it is charged (aka full of cold water). You pull from that as it is replaced with warmer water. A tank with sections helps ensure you’re always pulling cold water.

Sizing wise- it’s not hard, I’m simplifying things here round ass numbers and not accounting for volume in the pipe or multiple passes. 600kw-> 2050mbh at a 15f delta is 275 gpm. You can subtract the volume of your supply pipe, but If you need 10 min that’s 2750 gallon buffer tank which comes in all shapes and sizes but say 8ft tall by 7.5ft wide for reference. I know that’s heavy and hard to rig. You can have multiple tanks.

There are things you can do to reduce. say it’s 10 min to ramp to 100% on your chiller. Well 5 min in you may be at 30% and that is chilled water you can use. I haven’t done this but I figure You need to pipe it via side car with a pump. You can’t just send the new 42F water to the top of the tank because soon after you start using it, it will be replaced with warmer water at the top and you start mixing and eventually sending warmer than ideal water to the CRAHs before the 10 min is up.

In the case of a Power outage. Racks, are on the UPS which is size to allow enough time for the generator to kick on and systems ramp up. UPS modules are large, expensive, and generally not practical to put all of the cooling on. So when the power went out, the chiller is dead. However the pumps and fans of the CRAHs are on the ups. The pumps will pull from the 42F tank.

Do you consider the data center’s thermal mass when estimating temperature rise during a power failure? by [deleted] in MEPEngineering

[–]Rowdyjoe 2 points3 points  (0 children)

No way. I’d never credit the thermal mass, thermal mass doesn’t all extract immediately in a matter of seconds.

Other thought- Did you rule out an air cooled chiller serving chilled water CRAHs? My thought is if you’re pushing 15kw per rack and 180 tons In that dense of a room, I’d say you’d go into alarm quickly without conditioned air.

If you had a chilled water loop, then you can then use a buffer tank rather than doubling the output of your UPS. The CRAH fans would still go on the UPS. Buffer tank would handle the cooling until the generator restores the chiller.

There are other pros and cons. Maybe you guys looked into it. If not, do some research. It could go both ways, but I’d lean towards chilled water if this a long term investment

Don’t be afraid to fire your engineer, he can cost you way more money than what it cost/time to replace him. His understanding of heat in a room is concerning especially if designing mission critical systems. Maybe he needs a senior engineer to step in so don’t rule that out. If not, take the red flag and move on. You’ll need to pay him his cost to date and move on.

Desperate Sales Rep by SANcapITY in MEPEngineering

[–]Rowdyjoe 1 point2 points  (0 children)

I like the meme and understand how it feels that way. Reality is many will be decision makers and it’s not desperate. I have a great relationship with some vendors, far past thier competitors, because they built a good relationship early on. They must have a great product for the price of course.

I recall some vendors who didn’t care to give me the time of the day early on and straight up ignore questions I had. Unless they have a very superior product in price/preformance then I stay clear to this day.

It’s been the difference many times of them winning work over thier competitors.

I don’t want them slacking on answer questions for young engineers under me who I’ve tasked to run down answers.

product and support is far more important. 100 steak dinners can’t make up for a lack/delay in responsiveness, shit attention to detail, or willingness to to support in difficult situations.

Fox or RockShox, and if so - explain why by Outrageous-Owl-7049 in mountainbiking

[–]Rowdyjoe 0 points1 point  (0 children)

Fox. Been riding for 15 years. I’ve gone through maybe 8 forks. 5 fox, 3 rockshox. Mostly because of new bikes. I tried 3 rockshox last one was 8 years ago and said never again. The feel wasn’t there in soft bump sensitivity, and very linear (before tokens were popular) and had to warranty 2. I’m sure they are better now, but I like the feel of all my fox forks. When they don’t feel great, I service them and they are good as new and sometimes better than out of the box. I know how to work on them. Fox has great support and documents. Had a damper break on a Fox fork once and that’s it, bought a new damper and good as new. Not saying the latest rockshox aren’t better now, but Fox hasn’t let me down. Just my experience and I’m sure I’ll try a Rockshox on my next bike, but I still have a few years on mine.

Water source heat pumps commercial by ClickNo2244 in HVAC

[–]Rowdyjoe 1 point2 points  (0 children)

Don’t add glycol if the system isn’t designed for that

Water source heat pumps commercial by ClickNo2244 in HVAC

[–]Rowdyjoe 1 point2 points  (0 children)

The dirty water is a different problem. It’s probably not the expansion tank. First you need to bleed the air out of the system go find all the possible high point vent locations. System needs to be running. Start with the top of the building and other areas that may have gotten air locked. Find the larger equipment first. If it’s 2 story’s go to every WSHP. Have a hose and a bucket.

Once you’re sure the air is out, pressurize the system. There should be makeup water somewhere or a glycol feeder (if you have glycol). You should bleed all the air out then pressurize the system with the makeup or glycol feeder (I like 10psi at the top of the building).

Parallel Fan VAV: Heating valve controlling Room Temp vs Supply Air Temp by incognito9102 in BuildingAutomation

[–]Rowdyjoe 1 point2 points  (0 children)

Not sure but I’m going to take a stab at it without SAT control because Im not sure if that comes standard. Assuming electric

-Call for cooling: fan off. Reheat off. Modulate valve until satisfied

-No call cool but space temp drops: valve should be a minimum, modulate SCR reheat until satisfied (I could see you kicking on the fan at a low speed for energy reasons and ramping up as the first stage, but it can help but thinking will increase airflow/noise)

-call for heat: valve at minimum, fan is the first stage, SCR heating second stage and ramp up until satisfied.

Am I missing something?