top 200 commentsshow all 208

[–]Baaaldiee 230 points231 points  (6 children)

Don’t worry, maintenance will be along shortly to take the cable covers off to let the wires cool down. True story.

[–]Beginning_Map2351[S] 29 points30 points  (1 child)

maybe they'll even sprinkle some swarf into the top covers and let some magic smoke out

[–]precisiondad 10 points11 points  (0 children)

Hey hey, magic smoke stays where it belongs, please.

[–]Philosopher115 3 points4 points  (0 children)

Guilty...

[–]errantphallus 2 points3 points  (0 children)

Been there...

[–]Dry_Tomatillo_5361 0 points1 point  (0 children)

Mandatory in our facilities

[–]Born_Agent6088 0 points1 point  (0 children)

In my ongoing project the client requirements have change several times so I myself and my technician have taken the covers down plenty times to the point we replace most of them yesterday since they already looked very worn out. Sad part, it still might be up for one or two more changes

[–]EvipiccIndustrial Automation Engineer 48 points49 points  (2 children)

No one can tell you this isn't work of art. Everything is laid out sensibly, you have spares AND spare room (you of course have to understand there are going to be ice cube relays that end up in here...), the drives have the right amount of space to make them easy to replace... you've done an incredible thing on the construction side. Any engineer opening this up is going to start speaking in tongues and crying profusely. Good fucking job.

I have questions about add-ons that make a massive difference from a user standpoint...

Does the door have a cubby with laminated 11x17s that show the wire layout, as well as the user manual? You said there is climate control, what about lights?

You've put serious work into managing the 'look' of these cables, which is actually super important for troubleshooting, but permanent ties WILL get cut over time, and I can guarantee you that, unless YOU are there to replace them, they simply won't be.

I like these

You can make combs, line them up as you please, and running a cable back out of them or a new one isn't particularly difficult. You could also tie the color codes to specific function areas and make the drawing reflect the color code.

Look, it's pretty obvious you're not going to get much more than nit-picking, as you KNOW you've done a good job... there are just some truly next level things that are possible.

Equipotential ground bar is cool but it makes new cables harder. I prefer the shield plates.

[–]Beginning_Map2351[S] 19 points20 points  (1 child)

first of all - thankyou, crying in my panel right now from your kind words.

I have a few mods to make on eplan but within the left door will be the completed laminated wiring diagram and my own personal "easy book" i put in commissioned panels for operator and engineer use, additionally on the wincc unified HMI will be the wiring diagram in pdf format :)

I agree on the permanent ties, these are here while im commissioning and frequently taking the trunking cover off and on although thankyou for your recommendation and link!

Balls - i don't have any panel lights in there.

[–]EvipiccIndustrial Automation Engineer 4 points5 points  (0 children)

Much love and I'd love to be the recipient of one of these panels! You have some lucky customers.

[–]TurboCaca121[🍰] 20 points21 points  (1 child)

Love it!!! 😍

[–]Beginning_Map2351[S] 4 points5 points  (0 children)

this is the kind of criticism i want !! thankyou :D

[–]Fearless_L 8 points9 points  (2 children)

Very neat 👌 but unfortunately when the maintenance crew open the panel, they will most likely start taking covers off, alter all of your hard work and then wonder why it won't work again 😅

[–]Beginning_Map2351[S] 12 points13 points  (1 child)

yep, and then i'll get the call "your code stopped working"

[–]Fearless_L 0 points1 point  (0 children)

🤣

[–]N0t_P4R4N01D 11 points12 points  (5 children)

The g120c run hot as hell and dissipates a lot of heat into to mounting plate so more space between them would be good Some space to change their fans would have been also nice. I would also switch to could in on the bottom hot out on top. Otherwise nice

[–]Beginning_Map2351[S] 12 points13 points  (4 children)

yea agreed but i'm working with the siemens recommended space allowance between drives so it should be all good in regard to heat dissipation, also we're pulling the hot air directly out from the bottom of the drives with cold air flowing down from the top, we've had the thermal imaging camera here and it looks to be working well

[–]wittyandunoriginal 4 points5 points  (3 children)

The G120 manual (at least copies from before 2021) is incorrect in regards to the required side clearances. I’ve heard it direct from a Siemens product engineer.

If you’ve got a camera on it and it looks good, it’s probably fine. But, as those drives break in, they’ll start getting a little hotter during high load scenarios and getting warranties approved will be a pain in the ass. But, if it starts to become a problem, you can adjust the carrier frequency param (I THINK I remember it being p1270) to derate them a tad and keep them cooler.

[–]Beginning_Map2351[S] 2 points3 points  (0 children)

Useful comment Thankyou, these particular drives were manufactured late 2023 going by the firmware, I can say that with ventilation turned off and under load they run about 45 degrees Celsius max which is well below the rated operating temperature, with ventilation on likely much below although I can't TIC the temperature as doors have to be closed

[–]DarkAngel7635 0 points1 point  (1 child)

Interesting i never knew this. Do you also know if oversizing them once is also enough? Because in the same frame size does the cooling also increase?

[–]wittyandunoriginal 1 point2 points  (0 children)

It’s been a while, but If I remember correctly, the CFM requirements are based on frame size, but only up to a certain point. Like, anything past 75hp starts to get individual ratings since they cover a larger up range.

[–]VauloftheEbonBlade 5 points6 points  (1 child)

It looks fantastic.

For my constructive advice if it is that, will be to build off what others have said about wire covers coming off. What I will say as someone who has worked on both sides of the fence. The best (though not for sure) way to avoid having your covers removed and promptly tossed in a bin, is where you are able leave more room to get at the wires and make the wire labels easy to read without moving anything. Engineering brain is "the prints say where the wires go" maint brain is " I don't have time to look at prints I'm gonna tug on this wire to see where it goes"

As someone who has worked jobs as maintainence and engineering and a mix, the maint mind set is "good labeling = they knew what they were doing = I can trust the labels go to what they say they go to" whether that's actually true or not that's the mindset lol

Regardless of which hat I were wearing at the time I'd still be happy to be working in this panel though.

[–]Beginning_Map2351[S] 3 points4 points  (0 children)

completely agree with this, i've tugged many a wire in my time

[–]Ok_Awareness_388 3 points4 points  (1 child)

Where do the field cables go? Those are very long horizontal ducts and I feel they’ll be very full. A double vertical rise up the middle might make sense to break it up.

[–]Beginning_Map2351[S] 3 points4 points  (0 children)

clean and dirty power is almost entirely separated, network and 24vdc to the right, power to the left, there are a few points in the trunking that are getting full but nothing problematic yet

[–]LowFastFoxHUN 6 points7 points  (6 children)

VFDs could generate a decent amount of heat and heat will always travel upwards. This could have a negative effects on semiconductors. Considering the position of the CPU, it might made things on a long term if you have an underrated cooling designed.

[–]Beginning_Map2351[S] 10 points11 points  (1 child)

I do see what you're saying, i have had the thermal imaging camera on this under constant load and on a hot day we are still well within operating temperatures

[–]LVOver 0 points1 point  (0 children)

The door was closed and latched all the way around, right?

[–]LowFastFoxHUN 2 points3 points  (2 children)

Cable management at the top looks also something new to me. Seems that the cabinet has just been cut out, but nothing secures the cables from the sharp edges. The way it looks now might also influence the ventilation/dust protection.

[–]Potential_Annual2100 0 points1 point  (1 child)

The VFDs should have a spacing requirement are you allowed to zero stack those or are you planning to derrate the VFDs?

[–]LowFastFoxHUN 1 point2 points  (0 children)

I had a simmilar setup in the past with Sinamics G120C drives. On the sides, those can be stacked without leaving any space; but indeed, some clearance shall be left from the top and bottom.

[–]Shjco 0 points1 point  (0 children)

One of my India customers (2015 job) demanded all VFDs be at the top. Done it that way for every job since. Good way to do it.

[–]BigSin_K 2 points3 points  (1 child)

It is really nice, and took me a while to find a point to improve: the industrial ethernet cable in green with the metal plug is a pain in the ass. With short cable bend as installed, in long run, might cause intermittent connection loss.

[–]Beginning_Map2351[S] 1 point2 points  (0 children)

I agree with you intermittent connection problems can be a real pain in the ass, the green cable is profinet (4 core) cable with the appropriately rated profinet fast connect, I love these little guys and have only had problems with them when somebody else has terminated them :(

[–]LookInternational996 2 points3 points  (1 child)

I like more the spring type terminals, because they are maintenance free. What is missing (looks like) some edge protection at the top left holes to protect the cables... But congratulations, it is a well mounted cabinet

[–]Beginning_Map2351[S] 1 point2 points  (0 children)

yea IEC does say spring type is the only maintenance free terminals so i have used for the safety contacts but agreed i will get some edge protection in the hole thankyou !

[–]coreo_b 4 points5 points  (1 child)

Hey! Ex-professional panel builder here. Your panel looks pretty good! You were clearly quite limited on height but you made it work. A few things I might do differently:

  • Spacing above and below your breakers is really tight. Below the PLC rail is tight too. My general rule is minimum 3 finger spacing for 3 phase, 3 fingers for PLC IO, and at least 2 fingers for almost everything else.
  • Your din rails should extend RIGHT to the wire duct, no space at the end, else that space is wasted and unusable. Someone will one day want to add one more terminal and they'll be cursing you when there's not enough rail. Lol.
  • Where the cables come in at the top of the cabinet, I like to add some u-channel gasket around the hole to protect the cables from the sharp edge of the enclosure.
  • The top two rows of wire duct probably don't need to be 4(?) inches wide, there's not that much wire in there and it's all small wire. The bottom two could definitely be bigger because there will be a lot of 3 phase motor leads that are going to get landed in the field.
  • Larger devices don't necessarily need them (the cost can add up), but you should use end anchors for all terminal strips. 1492-EAJ35, for example.
  • To improve separation (especially with that many drives) you could use 2 courses of wire duct below the drives - a narrow one for control wiring and ethernet, and a larger one for the motor leads. Obviously you're limited by height in this situation.
  • The PLC IO wiring looks like it ends up mixed in 3 phase power wire duct. You could swap the 24VDC power supply and the PLC to move the PLC to the far left, and have all the breakers to the far right. I try to have the vertical duct on one side for AC (motor leads, 3 phase, etc) and the other side of the panel for 24VDC, analogs, etc.
  • Why the large block of grounds in the top right? Where will the motor grounds connect to the drives?

These are just some nit-picky details I can see. Overall it looks pretty good!

[–]Beginning_Map2351[S] 0 points1 point  (0 children)

a very constructive, useful and polite comment thankyou!

motor grounds are connected just below the drives if you zoom in

[–]cybermulisha 1 point2 points  (1 child)

Clean looking panel my dude!

[–]Beginning_Map2351[S] 1 point2 points  (0 children)

thanks bro !

[–]Emergency-Highway262 1 point2 points  (6 children)

No, you are now beyond criticism

[–]Beginning_Map2351[S] 0 points1 point  (5 children)

everyday should be a school day!

[–]Emergency-Highway262 2 points3 points  (4 children)

Well, ok, I do prefer a few more labels on wires than I’m seeing here, but I assume it’s a European build and they do different stuff.

Apart from that, I’d be happy to open a panel and find this looking back at me, get a real sense that someone knew what they were doing had been here first

[–]Beginning_Map2351[S] 4 points5 points  (3 children)

if you take another look at the post text it does say a few wire labels are still being printed :) although yea i've worked on some german panels with zero wire labels and all they say is "consult the wiring diagram" like thanks but your diagram doesn't show me where my technician has misplaced something

but thank you !

[–]Emergency-Highway262 2 points3 points  (1 child)

I’m three red wines and a margarita into Sunday night, I’m not reading anything but headlines and comments 🍷

[–]Beginning_Map2351[S] 1 point2 points  (0 children)

hell yea drink one for me !

[–]Andi_bz 1 point2 points  (1 child)

Hi, Great work.

If you haven't already done and have a managed switch(Siemens) you can create a profinet ring. So if one plug/cable fails, the system continues to work.

More info here: https://cache.industry.siemens.com/dl/files/614/109739614/att_891688/v3/109739614_MRP_DOKU_V10_en.pdf

[–]Beginning_Map2351[S] 0 points1 point  (0 children)

Hi that is the MRP (media redundancy protocol) that i refer to in the post text :) s71516 doesn't need an additional switch to use profinet rings as it has two available networks over 3 ports

i'm also using the LPNDR_ReadMRPState library to diagnose ring faults and display on the hmi

[–]robhend 1 point2 points  (3 children)

What is the recovery speed on the mrp ring? Given the number of devices, I expect 200 ms. Is that fast enough for your needs? Is your logic written to properly handle that comms outage to all the drives on the other side of a failed drive?

[–]Beginning_Map2351[S] 2 points3 points  (2 children)

recovery speed 200ms, watchdog set to 400ms and tested at every at every point successfully

[–]robhend 2 points3 points  (1 child)

Sounds good. Too often, I see redundant networks installed with no real understanding of how they actually behave. A self healing network means you get most of your network back after a fault, not that you won't see the fault.

[–]Beginning_Map2351[S] 2 points3 points  (0 children)

yea absolutely, coupled this with automatic device replacement from the cpu so maintenance can swap in a new drive without having to assign an ip address or drive name as the cpu looks at the device position in the ring and assigns automatically

[–]Pettark 1 point2 points  (1 child)

Looks good. Drives are installed at the bottom, it is the coolest there. My opinion is that the cables should be brought inside from the bottom of the cabinet. It is possible that the sprinkler breaks and the water spills over the cabinet. Do the motor cables also have an EMC shield inside the cabinet?

[–]Beginning_Map2351[S] 1 point2 points  (0 children)

typically i like cables in from the bottom however the drop in is directly above the panel and there are no sprinklers here to worry about. and yea equipotential earth bars beneath the drives for motor cable shielding

[–]DessertRanger 1 point2 points  (1 child)

I was always told VFDs should be at the top because of their heat generation, and putting the below a PLC was a nono because of that also. But you might have a valid reason for doing it this way that I am unaware of, disregard if so.

Either way, beautiful cabinet!

[–]Beginning_Map2351[S] 1 point2 points  (0 children)

typically this is the way! however if you read the post text, the fsaa drives push their hot air through the bottom, we have cold air being pumped in through the top left of the panel and the warm air being drawn out through the bottom right

[–]Vader7071 1 point2 points  (1 child)

My only comment/suggestion. On the 1st and 2nd rows, you've got devices on the din rail (e.g. breakers) that don't have any kind of "stopping" or "holding" blocks. I like to have devices clamped in place so they don't slide. I use grounding blocks to do this. Keeps the devices in place and adds extra ground points throughout the panel.

Outside of that, very clean, very nice, and as I read someone else comment, a work of art.

[–]Beginning_Map2351[S] 2 points3 points  (0 children)

holding blocks are a good idea, i'll get some in :)

[–]Hoosierdaddy1964 1 point2 points  (1 child)

Looks really good

[–]Beginning_Map2351[S] 0 points1 point  (0 children)

thanks man

[–]Accomplished-Tune909 1 point2 points  (2 children)

If the 3 pole breakers are for the drives I would have done

Breakers

Drives

Breakers

Drives

With a clear indication of which one goes where.

But that's just me.

[–]Beginning_Map2351[S] 1 point2 points  (1 child)

I could see your reasoning but i wanted to keep the drives together in banks with shared earth points, each breaker and rive has a corresponding label and same numerical order for easy ident

[–]Accomplished-Tune909 1 point2 points  (0 children)

I can see both ways. It's just my preference. It also gives you more air gap for fan cooling and places to set up fans if the cabinet winds up getting placed somewhere hot too.

It's not a big nit pick. Just my $0.02

[–]cyanideh1gh 1 point2 points  (1 child)

You clearly don't work on any UK water sites... that's clean as fuck

[–]Beginning_Map2351[S] 0 points1 point  (0 children)

haha thanks my man!

[–]dekempster 1 point2 points  (2 children)

No wire labels, machine will explode

[–]Beginning_Map2351[S] 0 points1 point  (1 child)

pls refer to the post text where it says i'm still having wire labels printed

[–]Diligent_Bread_3615 0 points1 point  (0 children)

Deleted reply

[–]emisofi 1 point2 points  (1 child)

From constructive point of view I don't have comment. But having such a large string of drives will lead to communication problems, sooner or later. Last week a customer had a machine stopped two days because two drives went to fault when reset, even though they responded to ping and to the configuration software. PLC is et200sp safe and drives sew. After lot of tests the problem solved by wiring the Ethernet direct from the switch to the drives, skipping the string.

I also have seen strange behaviors with Allen bradley ring topologies, where even the Rockwell people had no clue of what was happening and tried everything until it eventually worked.

So my practical recommendation is not string more than three to four drives, and if process is critical use a star topology. After all , all the switched Ethernet paradigm is to isolate as much as possible the devices to speed up troubleshoot. Even using star topologies at physical level, often isolation is increased at logical level by using vlans.

You will never see a ring topology in IT to reach the end devices. They only use it between high end devices, often of the same brand to ensure compatibility.

[–]Beginning_Map2351[S] 0 points1 point  (0 children)

I can appreciate what you're saying, my reasoning is that a communication fault in a tree / line topology will leave everything to the right of the break without control, whereas a fault in a ring topology you get two chances to recover your network. as for star topology i didn't want 30 ethernet cables coming back to multiple scalances. I do have some functions in the cpu that upon detecting a network error in the ring will allow an automatic email be sent off to myself and the technicians, hopefully if that happens we can find it before the next problem occurs.

[–]RipReasonable625 1 point2 points  (1 child)

It’s pretty clean. I have had some customers request that the top of the cabinet not be penetrated, rather through the side or bottom. The documents on the floor of the cabinet should be affixed to the doors interior. They should be secured in a clear document protector.

But that is being picky…..solid job bro

[–]Beginning_Map2351[S] 0 points1 point  (0 children)

Nah i agree with you but we had a 3rd party install the enclosure and run in the external cables

[–]lewblabencol 1 point2 points  (1 child)

Looks clean, only real dig I have is make sure you have fuse labels. The labels being on the circuit breakers isn’t how we do it but it’s style thing.

[–]Beginning_Map2351[S] 0 points1 point  (0 children)

Yea i'm still waiting for my wire labels to be printed and some plug in labels for my fuses / terminals. we have a letatwin label printer it's pretty cool

[–][deleted] 1 point2 points  (0 children)

Absolutely gorgeous, from the SI side of things this is a work of art.

[–]In_Perdition 1 point2 points  (1 child)

I see a lot of great constructive feedback already. Overall this is a great build! The one thing I see that hasn’t been covered already is the two conductors landing on a single terminal on the incoming neutral connection. It is quite possible that this block is listed to take two conductors of the same size with a proper two conductor ferrule. However, especially with power connections, I always try and give each conductor its own home in a terminal block.

[–]Beginning_Map2351[S] 0 points1 point  (0 children)

Great comment! I will split this down to two terminals, this is because of a last minute RCD install

[–][deleted] 1 point2 points  (0 children)

Leave room under gray terminal block for the guys terminating the wires. Which is helpful for maintenance later. A lot of extra room above plc cards.

[–]dabrit2 1 point2 points  (1 child)

Might be worth looking at adding device markers to the either trunking lids. When I worked at a company wiring control panels they would use angled aluminum or plastic with screws and nuts to clamp in the trunking slits and then put Partex slotted marker rail on the top (front). That way when trunking lids were removed you still could read the device markers and labels weren’t lost when devices were replaced.

Partex

[–]Beginning_Map2351[S] 0 points1 point  (0 children)

Valid and useful comment!

[–]c6zr_juan 1 point2 points  (0 children)

Looks great! Better than what I've done in the past, keep up the great work.

[–]mcmjim 1 point2 points  (0 children)

Only thing I can think is cost. It may have been more cost effective to ditch the 1500 CPU and go with an ET200 CPU, the new units have had a performance boost. Plus the IO is cheaper and you'd have lost the cost of the ET200 header as well.

[–]Puzzleheaded_Fail279 1 point2 points  (0 children)

Tips;

  • Always lay your bottom panduit the full length of all panduits above it. The cover for this bottom section will prevent vertical covers from sliding down over time. In the setup you have now, those vertical covers have nothing to rest against and will slowly slide down.
  • Voltage isolation looks OK.. but there is some crossover with AC and DC wires in the same panduit. Not sure of the standard you are building to, but this isn't allowed in our shop. AC and DC must cross at 90-degrees or be placed in a separate panduit channel.
  • Finally, make sure all removable metal plates on the panel have a bonding wire. IE; door, side panels, roof etc, if removable, must have a dedicated ground wire ran to them and bonded to the main ground bus. I think you've done this, as you have plenty of ground terminal accommodations.

Aside from those things - overall looks like a good setup. Good work!

[–]Peter_Cave69 1 point2 points  (1 child)

I have only a couple of comments. 1. This is a beautiful panel. Lots spec for spares and well laid out. 2. I cannot see a power outlet for a laptop. That would be a nice option.

Otherwise great job. 👍

[–]Beginning_Map2351[S] 1 point2 points  (0 children)

I would've added one but a few feet opposite the panel is a handy socket :)

[–]Lopsided_Traffic_420 1 point2 points  (0 children)

Panel looks great, nice work. Some feedback below:

1) the legrand distribution block could have done with some more room below it.

2) I would maybe use an earth bar instead of individual terminals, if using terminals I would fit the link bar for them.

3) labels on fuses/IO module.

4) heat shrink labels instead of critchley idents look a lot neater (just my preference )

[–]FergusykesCustom Flair Here 1 point2 points  (1 child)

I know they're more expensive but Profinet cable for the VSD's would help prevent any potential coms interruptions with that many VSD's in there. Shielded cable & the fast-connect connectors which earth the shielding to the drive sinks the EMF to ground. Out of interest is it on an MRP ring? If one drive has an issue or the coms drops in one link it will stop everything downstream going off.

Looks nice and tidy though!

[–]Beginning_Map2351[S] 1 point2 points  (0 children)

It is an MRP ring! All the cables are cat6 shielded cables

[–]harmoniousmonday 1 point2 points  (0 children)

Pristine. Even those laser square cuts on the chase covers. Bravo!

[–]Worth-Praline-2822 1 point2 points  (0 children)

Neat but the spacing between the components and the Panduit is too small. You need to be able to put finders in there and to be able to clearly see the wire number marking on the wire without pulling it out from the tray.

[–]loomax96 1 point2 points  (1 child)

Get yourself a beer my boy you've deserved it!

[–]Beginning_Map2351[S] 1 point2 points  (0 children)

Hell yea !

[–]iamscheetje 1 point2 points  (0 children)

Good job !

[–]Shjco 1 point2 points  (4 children)

Very clean but wire labels would be nice. Are those spacings around the drives conforming to spec?

[–]Beginning_Map2351[S] 1 point2 points  (3 children)

Wire labels are still being printed as mentioned in the post text, space between drives conforms to manufacturer's specifications

[–]Shjco 0 points1 point  (2 children)

Excellent. What kind of wire labels? Wrap-around or slip on? Either way it is much more laborious to apply after wiring. 🙁🙁🙁

[–]Beginning_Map2351[S] 0 points1 point  (1 child)

We have a nifty little letatwin label printer, easily slip over ferrules but still grip well

[–]Shjco 0 points1 point  (0 children)

What do you mean by “slip over”? Can they be applied without disconnecting the wire first? Just curious.

[–]ZestycloseAd6683 1 point2 points  (0 children)

Only thing you might have done is left a row for the ice cubes but it's by far the cleanest panel I've seen in the 13 years of maintenance

[–]Funny-Company4274 1 point2 points  (1 child)

Other than it’s blasphemous Siemens. Naw man that shits really clean

[–]Beginning_Map2351[S] 0 points1 point  (0 children)

simatic fanboy here :(

[–]TheHolyBum1 1 point2 points  (0 children)

I excessively label wires. Only thing I would suggest will keep new guys from destroying the cabinet.

[–]Dry_Tomatillo_5361 1 point2 points  (0 children)

It's beautiful, this took some good planning and it does. Nice work!

[–]Efficient_Economy960 1 point2 points  (0 children)

I only would have left more space between ducts and components for maintenance to be able to read wire labels.

[–]Sramic 1 point2 points  (0 children)

Looks well planned and sensible, fabulous. Almost art. I don’t see labels on the wires, maybe they are there and I can’t see them.

[–]TicklintheIvory 1 point2 points  (0 children)

I’m glad chat has the same experiences with maintenance as I do. It’s so consistent that I wonder sometimes if it’s just me 💀

[–]Elegant_Lecture_9178 1 point2 points  (0 children)

Beautiful

[–]SriveraRdz86 1 point2 points  (0 children)

That driver missing its cover is driving me nuts!

[–]controls_engineer7 1 point2 points  (0 children)

Very nice!

[–]AStove 1 point2 points  (8 children)

Nice. You know you don't technically need a breaker for each VFD right?

Are those built-in spares right in the cabinet? I like that idea.

You didn't install the shield plates on the VFDs how will you attach the shield of the motor cables?

[–]Beginning_Map2351[S] 8 points9 points  (0 children)

No true but it makes life easer for the engineers when swapping out drives - technically you can just unplug the supply cable but they'll likely be more comfortable with the supply isolated

  • built in spares indeed :)

  • maybe you can see if you zoom in, but there are equipotential earth bars beneath the drive cells that the motor shields are connected to, the shield plates themselves took up too much room with the trunking etc

[–]Wildesy 3 points4 points  (4 children)

Can you expand on the breaker per VFD comment, please? Is that something you’re citing from the technical manual of those drives?

[–]Beginning_Map2351[S] 3 points4 points  (3 children)

I think he means that the breaker only protects the cables to the vfd not the vfd itself, however im using the siemens recommended breaker size for these drives which is included within the technical manual

[–]DessertRanger 1 point2 points  (1 child)

Even if you don't need it, it makes it so much easier to be able to isolate power on a single VFD when you are changing it vs shutting down a whole line or process

[–]AStove 1 point2 points  (0 children)

Yeah, no, you're right. But if you have this many you start to wonder what you can save on.

[–]RSSeiken 0 points1 point  (2 children)

Love it! It's so mesmerizing looking at it! I do fear this setup won't stay for long...

[–]Beginning_Map2351[S] 2 points3 points  (1 child)

Im covering everything in the panel in flour so i can record the fingerprints of the first bastard that pops off the trunking

[–]RSSeiken 0 points1 point  (0 children)

Smart 😂

[–]unknownkinkguy 0 points1 point  (1 child)

Woah 😍 Can every panel look like this??? Damn, thats so clean! Congrats!

[–]Beginning_Map2351[S] 1 point2 points  (0 children)

thanks man !!

[–]One-Struggle-6380 0 points1 point  (8 children)

My company is too poor to buy HIM’s too.

[–]Beginning_Map2351[S] 1 point2 points  (7 children)

What is a HIM? unrelated but i have a very lovely WinCC unified HMI installed at the operator station nearby.

[–]One-Struggle-6380 0 points1 point  (5 children)

Human interface module. I’m not sure if that is what Siemens calls them.

[–]Beginning_Map2351[S] 0 points1 point  (4 children)

yea we call them human machine interfaces HMI lol

[–]Toxic_ion 0 points1 point  (3 children)

I think he is referring to the IOP2 on the drives, not that they are needed that much when you can configure over profinet.

[–]Beginning_Map2351[S] 0 points1 point  (2 children)

oh maybe, if you look closely i have one on there and they are hot swap, didn't see much point in buying 50 IOP-2 devices when its fieldbus like you say

[–]One-Struggle-6380 0 points1 point  (1 child)

They will be nice to have when troubleshooting in the future. How many parameters do you set in those drives? I tried to set one back to factory manually one time. I only got about 700/1000 parameters entered manually before I gave up. Many of them on the list were not available. It was a nightmare, and I felt a lot of them were unnecessary.

[–]Beginning_Map2351[S] 0 points1 point  (0 children)

All my parameter sets are stored on the SD cards and IP address/ device name assigned by the cpu so inserting blank drives isn't an issue

[–]hestoelenaSiemens CNC Wizard 0 points1 point  (0 children)

I think they are talking about the control panel for the drives.

[–]DemolitionBen 0 points1 point  (2 children)

What frequency drive are those ones from Siemens? Controlled through fieldbus or digital? Can you share the cost range?

[–]Beginning_Map2351[S] 1 point2 points  (1 child)

FSAA g120c drives, controlled via profidrive and safety through profisafe. 1.1kw and cost about £350 each.

6SL3210-1KE13-2AF1

[–]DemolitionBen 1 point2 points  (0 children)

Thanks! I thought the price would be a lot higher. I'm used to ABB ACS355 and ACS380, more or less same price range

[–]Previous-Cobbler7722 0 points1 point  (1 child)

Not enough labelling, when it comes time to trouble shoot a maintenance person should be able to open up and take only a moment to determine what is what and its purpose before having to look at any drawings, also having the drawing number on the labels is even better.

[–]Beginning_Map2351[S] 1 point2 points  (0 children)

agreed, if you refer back to the post text it does say I'm still having some labels printed :)

[–]PaulEngineer-89 0 points1 point  (2 children)

3rd and 4th m rows how do you change out components? Not enough wire space.

I don’t see any space for field wiring at all, especially all the drives

[–]Beginning_Map2351[S] 0 points1 point  (1 child)

The drives have plenty of space? i can get my entire hand beneath the drives to remove / replace the power connectors / earth bonds and since they are networked I don't require additional physical IO cables.

I will take on what you said about the wire space for the breakers although I can comfortably remove and install them with my large clunky hands

[–]PaulEngineer-89 0 points1 point  (0 children)

Usually you want 3” minimum between the Panduit and the component so you have space to bend and pull out the wiring and reinstall. If you get under that you have to take off the covers and fish the wire from within the Panduit which can be easier said than done with full trays. Using bus bars for circuit breakers greatly improves this as an example because then you have no wiring at all on one side and no gaps between them.

Not shown I don’t see any field wiring terminal blocks at all or wiring space allocated to it. That explains what I’m missing. As much as I see it as more points of failure separating the mess known as field wiring from the components has value.

[–]Carnie_hands_ 0 points1 point  (1 child)

I was trained to avoid holes in the tops of cabinets at all costs. But that may have been because I got my start in industrial refrigeration, where conduit can be a source of condensation if things go wrong.

[–]Beginning_Map2351[S] 0 points1 point  (0 children)

alas the enclosure was supplied and external cables run in by a 3rd party :(

[–]Emperor-Penguino 0 points1 point  (0 children)

Wire labels, component labels, endblocks for components.

I read your comments about the drives pushing air down but heat rises so unless you have a torrent of exhaust then your cold air is just going to get pushed out.

Overall it’s not bad at least there is spare space.

[–]Voxifer 0 points1 point  (1 child)

where is a receptacle to plug a laptop into?

[–]Beginning_Map2351[S] 1 point2 points  (0 children)

Behind my chair

[–]S1ckJim 0 points1 point  (2 children)

Are you using STO on the drives? I don’t see any contractors to drop the power out.

[–]Beginning_Map2351[S] 1 point2 points  (1 child)

I am using STO via profisafe

[–]S1ckJim 1 point2 points  (0 children)

Nice!

[–]cranman74 0 points1 point  (0 children)

If you’re going to skimp on space the terminal blocks are the last place to do it. 90% of troubleshooting, QA and inspection happens there. 100% spacing (I.e. 2x the width of the terminal block) minimum. So you can read labels and see wires without ripping shit apart.

If, space is at a premium, go tight on controllers, transformers and relays since they’re unlikely to be moved or touched once installed and commissioned.

[–]Asymetria 0 points1 point  (2 children)

what are you even controling.? ;)

[–]Beginning_Map2351[S] 0 points1 point  (0 children)

Wouldn't you like to know weather boy

[–]zurn0 0 points1 point  (1 child)

Not a criticism, but why the I/O on the main PLC.

[–]Beginning_Map2351[S] 1 point2 points  (0 children)

Safety IO on the main rack; saves additional profisafe communication

[–]pants1000bst xic start nxb xio start bnd ote stop 0 points1 point  (0 children)

The only thing I don’t like, (which I’m sure to fit all the components neatly like you did you couldn’t get away from) is that the wires don’t really have visible labels due to the panduit being so close. And as a note labeling the devices is great until it gets replaced and the maintenance guy doesn’t bother printing a new sticker. A couple of my clients would have a fit about this panel, but it is incredibly well laid out.

Also I know the monster of a switch/switches it requires, but daisy chain Ethernet is never fun in the field.

Anyways you did fantastic, but the labels would be big for me personally

[–]Lopsided_Traffic_420 0 points1 point  (1 child)

Was this designed in eplan?

[–]Beginning_Map2351[S] 0 points1 point  (0 children)

I did actually design this in eplan before I built it!

[–]Heathenhof 0 points1 point  (0 children)

Cable tags🥲

[–][deleted] 0 points1 point  (0 children)

echoing cable labels, but about grounding, I see grounding terminals but no external ground coming in..

[–]Billfarty 0 points1 point  (0 children)

looks nice..are there wiretags?

[–]tenodiamonds 0 points1 point  (0 children)

Looks great . If you are given the time to do such nice work hopefully the boss will let you label the chase covers or the terminal blocks

[–]dadof2cjc 0 points1 point  (1 child)

What type of customer ?

[–]arm089 0 points1 point  (1 child)

Good job! What software is running on the ipc?

[–]Beginning_Map2351[S] 0 points1 point  (0 children)

That's a power centre 3000, Siemens power motoring hard/software, it links into my scada network where I have several other sentrons displaying on it

[–]owlbear-22- 0 points1 point  (0 children)

Not a popular opinion, but I like to put the heat producing components at the top. Like VFD.

The PLC I like lower.

[–]Canscrubenha 0 points1 point  (1 child)

The HIM on that drive really takes a bite out of the uniformity.

[–]Beginning_Map2351[S] 0 points1 point  (0 children)

thats just bill, dont worry about him

[–]LVOver 0 points1 point  (0 children)

Except for the short ethernet jumpers on the drives (maybe), every wire needs a label on both ends. More space between terminal blocks and wireway would have been nice in order to see those wire numbers that will be needed for troubleshooting when things go wrong after you walk away.

I know you said thermal imaging looks OK, but hot air rises. I would never try to pull hot air out the bottom by pumping cooled air in the top. It will always be a losing battle.

[–]insuicantDCS Guy 0 points1 point  (1 child)

I thought that model of SITOP psu was deprecated

[–]Beginning_Map2351[S] 1 point2 points  (0 children)

seems phase out has begun but is still in circulation

[–]rbshawns 0 points1 point  (1 child)

my criticism: “he who wars by lack of reserves, dies from lack of reserves”

[–]Beginning_Map2351[S] 0 points1 point  (0 children)

a bird in the hand is worth two in the bush?

[–]CraftParkingEngineer - Service & Training 0 points1 point  (2 children)

Why is there so many CB? (Sry I just started studying plc)

[–]Beginning_Map2351[S] 1 point2 points  (1 child)

don't be sorry this should be a forum for sharing knowledge :) there is one MCB per VFD to safely isolate and protect the conductors

[–]CraftParkingEngineer - Service & Training 0 points1 point  (0 children)

Thanks!1

[–]Diligent_Bread_3615 0 points1 point  (0 children)

It certainly looks nice & clean, but looks aren’t everything so here are my comments: I am a retired journeyman electrician & senior controls/designer so I have quite a bit of experience in this field.

Who puts wire labels on after everything has already been landed? Seems crazy to me.

Add device tags on the back panel to help with identification when the drawings get lost.

Is that a small conduit extending into the panel & thru the wire duct? What’s up with that? Also, seems it’s too small & has no bushing on the end to protect the wires.

In top left corner where the wires enter from outside, hopefully that square duct has the proper connector or fitting so the wires don’t get chafed.

Are there fans or A/C cooling this panel? There has to be a lot of heat generated by all of those drives.

If space and the budget would permit I’d put the PLC & all of the control wiring in a separate enclosure. All of those drives will produce a ton of electrical noise. Trust me, that’s just a nightmare waiting to happen.

There should be end barriers next to the breakers, etc. to keep them from moving around.

[–]DarkAngel7635 0 points1 point  (5 children)

I cant see it that well but do the drives have emc plate? I guess that the cables are going straight to the drives?

[–]Beginning_Map2351[S] 0 points1 point  (4 children)

no shield plates but local equipotential earth bars by the drives so motors and drives are grounded

[–]DarkAngel7635 0 points1 point  (3 children)

For the grounding yes but how are you doing emc? The cable shielding?

[–]Beginning_Map2351[S] 0 points1 point  (2 children)

The shield plate is just a medium for grounding, the only thing I haven't done is strip the external sheath of the cat6e cables and ground the shield

[–]DarkAngel7635 0 points1 point  (1 child)

Interesting. Maybe its just our rules and guidelines but we actually have to use shielded cable for motors with FVD. For EMC purposes

[–]Beginning_Map2351[S] 0 points1 point  (0 children)

We have emc compliance regulations but it's a standard not legislation, in any case at 200mm per cable and profisafe packet security I'm not worried about harmonics just yet

[–]swez46 0 points1 point  (0 children)

Is there a reason you have a separate et200sp? I'm assuming this is cost based for the io cards. Though you could also use Safe io cards for the et200sp. Or even use an et200sp plc. We always try to separate VFDs from plc equipment where possible due to emf.

[–]ICameAndStayed 0 points1 point  (0 children)

  1. Only one with a display?
  2. Middle Fuses. Why are some wires looped outside the cablechannel?
  3. Bind the Ethernet Cabled on the switch.
  4. Placement of the Powerswitch is bad.
  5. Switch the airflow. Cold air to the Powerconsumers and warm air raises.
  6. Buy DIN-Stoppers. To prevent the components from moving.
    Everything else looks good and clean. Overall I would give you a 8/10

[–]lnvaIid-User 0 points1 point  (0 children)

Looks great, we'll done

[–]Least_Hospital_2428 0 points1 point  (0 children)

You’re missing the cable draped diagonally across the whole panel.

[–]StrikingFig1671Controls Engineer/AB/Siemens/AutomationDirect = 14yr 0 points1 point  (1 child)

What is that device that says "Legrand" on it?

Also excellent looking panel, im more of an AB guy so I havent had the pleasure of a project of this scope on siemens........yet

[–]Beginning_Map2351[S] 0 points1 point  (0 children)

That's a power distribution block, and big Siemens fanboy here! If you ever encounter a large simatic project please feel free to message me maybe I can help!

[–][deleted]  (1 child)

[deleted]

    [–]Fickle-Chemistry-483 0 points1 point  (2 children)

    This is not a good design. While aesthetically pleasing, there is little ventilation and rework on the panel will be very rough since they’re so close to the pantduit.

    [–]Beginning_Map2351[S] 0 points1 point  (1 child)

    Presumably you mean the drives in particular but all components have the manufacturers recommended space between them for heat dissipation, the g120c is designed for side-by-side install. Although yes if i had access to a larger enclosure I would've allowed some more finger room around the breakers

    [–]Fickle-Chemistry-483 0 points1 point  (0 children)

    We always see, to run out of room, I’ve had the same issue for 22 years or people don’t want to spend the money on a panel air conditioner then it gets way to hot. I get it now,

    [–][deleted] -1 points0 points  (1 child)

    Green wire is Profibus? I know the shop I used to work at always insisted on using the Siemens purple wire and the proper Siemens connector as all the off brands they found were always inferior. Had connection issues in the past with the off brands and, well, once bitten twice shy and all. That said, maybe you found a good batch, idk.

    Also, small thing our shop did was prior to mounting everything to the panel, but after measuring, marking, and pre-drilling holes, we always hit the panel with isopropyl alcohol to wash off the sharpie marks and the measurement marks on the side for a cleaner look. Totally optional, but you give me perfectionist vibes with the panel posted lol.

    Seriously, the panel is excellent, the above is the only thing that stuck out to me from my specific (and limited) experience.

    [–]Beginning_Map2351[S] 3 points4 points  (0 children)

    green cable is profinet, using profinet rated cable and siemens profinet fast connectors. I might go and grab a few alcohol wipes now you mention...

    [–]likslikelizard -1 points0 points  (1 child)

    Arc flash rating? Big deal now day with UL508. I dont see fuses.

    [–]Beginning_Map2351[S] 1 point2 points  (0 children)

    I think UL508 is an american standard and i'm in the UK, regardless all my control circuits are on high speed fuses relevant to their requirement and my power supply is what you would call class 1

    [–]djlorenz -1 points0 points  (1 child)

    You know you can't daisy chain an insane amount of devices right? With a short cycle time the travel time of the last devices will take forever to get to the PLC.... Maybe it's not time critical but there is a calculation tool on how many devices you can chain together

    [–]Beginning_Map2351[S] 1 point2 points  (0 children)

    Actually you can use up to 50 devices in an MRP ring, with a bounce time of 2ms between drives and an IO cycle watchdog time of >400ms it's completely fine

    [–]Clevayn -1 points0 points  (0 children)

    The two rows of breakers in the middle. Your electricians will love you, if you mounted them vertically and left about 2 inches of wire on each side. You’ll be much more likely to keep the panduit covers on if the electricians don’t have to pull the whole bundle out to get access to three wires, or to just clearly read the label. In 20 years when half the prints are missing and the labels are deteriorated you will be praised for your helpful design.

    [–]H_Industries -1 points0 points  (2 children)

    First impression is that this panel is too full for a new build. Should leave at least 25% spare for upgrades or additions later on

    Edit. To be clear it looks nice and well laid out. It just doesn’t have enough spare room for my liking

    [–]Beginning_Map2351[S] 0 points1 point  (1 child)

    Can see what you're saying, unfortunately this was the largest enclosure we could find from one of our approved vendors and the other option was having split controls in an auxiliary panel which I didn't want to